I have a lennox system that the compressor valves went out, I have got estimates to fix it which include from 1300-1600 dollars. So I have decided to fix it my self, but i cant find any thing out about the compressor.

It is a Copeland CR34k6-PFV-230. I cant find anything to match to that. I am assuming it is a 34,000 BTU so a 3 ton.

JOhnstone closest they have is a cr34kq-PFV-980wb.

So all in all can someone help me find an replacement?

Johnstone wont even give me a price because I am still in hvac school. So is there any OTHER Retailers to use?


By the way the low side was 150psi the high side was 130 psi

millerman
08-19-2004, 10:22 AM
Bring this issue up with your instructor, he/she may use your repair as a field trip and get it done with training. The instructor may have resources to purchase a compressor at your expense. Typically you cannot purchase refrigerant holding parts without an epa card. What info are you looking for as far as the compressor is concerned, other than where to purchase?

Edmund Forsthe
08-19-2004, 11:10 AM
why johnstone there are other supply houses try those.

ssscarpone
08-19-2004, 11:12 AM
What are some other places besides JOhnstone?

Steve Wiggins
08-19-2004, 11:14 AM
Your compressor is fine, you just have your guages on backwards. The red goes on the high side and the blue goes on the low.

ssscarpone
08-19-2004, 11:30 AM
I put the red on the high side (insulated suction line) and the blue on the low side the smaller copper tube.

And two other businesses said the same thing.

Edmund Forsthe
08-19-2004, 12:15 PM
like steve said the small copper tube is high red color and the large copper tube is low blue color. but feel free to replace the compressor without doing anymore checks on the system

stevehvac
08-19-2004, 12:32 PM
Blue=cold line
Red=hot line

Don't mix up the discharge with the liquid line if there are two ports.

swamp rat
08-19-2004, 12:55 PM
If the unit was running when you read your gages you still only had 20 lbs of differential - no matter how you connected to the unit. That's not good.
I like millerman's idea. It would be a good learning experience for everyone and the instructor might find the reason the thing failed in the first place.
Besides - you can use it as a sort of reverse pop quiz.

Shophound
08-19-2004, 01:15 PM
CR34K6-PFV-230 is 34,500 BTU at 45 saturated vapor/130 saturated condensing. Mass flow (lbs/hr) is 505.


CR34KQ-PFV-980WB is 34,000 at same specs. About 1 amp difference between the two at RLA, this model being the higher one. Mass flow 498.


You get to decide if these two differences are negligible or not. :D

Edmund Forsthe
08-19-2004, 02:00 PM
and the two other bussineses, i take two other tech were there and they aggreed on the prognosis, was this a free diagnostic? sound fishy to me

sonofdawra
08-19-2004, 02:22 PM
Also make sure that you have the valves closed in the maniflold before putting the gage set on the system. A common mistake for student learners is to have the high side short cycling directly back into the low side because the manifold valves are open.

AllTemp
03-17-2005, 11:21 PM
Originally posted by sonofdawra
Also make sure that you have the valves closed in the maniflold before putting the gage set on the system. A common mistake for student learners is to have the high side short cycling directly back into the low side because the manifold valves are open.

The new compressor would have presented the ame symptoms Ron, you took all our fun out of this...:-)

conrad1
03-18-2005, 06:16 AM
Originally posted by ssscarpone
I put the red on the high side (insulated suction line) and the blue on the low side the smaller copper tube.

And two other businesses said the same thing.

Why do homeowners still think they can do this themselves!
ssscarpone does not even know high and low

tinknocker service tech
03-18-2005, 06:42 PM
low side 150 high side 130 bad valves
i have seen a lot of bad valves and low side higher then high side maybe i missed class that day but never seen that
is it a heat pump in heat mode and your connecting to suction line and liquid line instead of suction port of compressor. on a lenox unit it is tucked up above the line set about 8 inches or on the compresser suction side about 6 inches from the compressor. i could see 110 low and 150 high if valves are gone totaly you would be equal or at least close. check you gages are the needles on 0
make sure they are not bipassing and talk to you instuctor
maybe he will make it a class efford. i know i would
if it is the compressor call lenox and get the right one for the unit also get the cap for it to. always change the cap and start capif one on any compressor or motor replacement