View Full Version : TRANE PCV-3J-C1-D2
pringlel
06-24-2010, 09:54 PM
Looking for any service information on this machine,
There is a sight glass on the first stage suction, what is this for? I think i am overcharged sounds like liquid hitting the first stage impeller when it loads.
klove
06-24-2010, 11:01 PM
Sight glass is to check vane operation and for the presence of carryover.
jayguy
06-25-2010, 12:16 AM
if it is a 2 pass evap and a 2 pass cond then at 44F leaving chilled water and 95 leaving cond water, you have about 380 tons @ 318 kW, 780# R11 and 7 gallons of oil.
and the sight glass is looking at the 2nd stage impeller.
acjourneyman
06-25-2010, 12:59 AM
It is probably just the vanes chattering.
pringlel
06-25-2010, 05:01 AM
Thank you all you have been a very big help. I see liquid refrigerant in the sight glass splashing up against the glass.
Jayguy thanks for the info extremely helpful.
Powered by vBulletin® Version 4.2.0 Copyright © 2013 vBulletin Solutions, Inc. All rights reserved.