View Full Version : 30GTN problem BI compressor



uboatcmdr
06-03-2010, 08:24 PM
:couch:I have a customer with a 30GTN100E631A It keeps tripping onT055 Compressor B1 failure Tried moving cpcs board to see if alarm would follow but it didnt HP and Lp switches look good and oil level is good. It has a Danfoss oil pressure control on the pecker head. i must be missing something any words of advice for a young chiller mech.

dmdrone
06-03-2010, 08:53 PM
The last one I had do that the HP switch was opening before it was suppost to You can watch it with your guages as it revs up

uboatcmdr
06-05-2010, 09:49 AM
I found a bad connection in the pecker head of the 06E comp. It was on the high pressure switch. One of those factory wire nuts that are crimped replaced all of the wire nuts and unit has cycled several times without incident.