in house worker
07-14-2004, 06:29 PM
I have a code that is "Bad Volts sen" this is word for word
This unit does not have any device that senses voltage drop
All 3 legs have 480-495 volt well with in the 10% drop.
Any ideas. It is locked out and wouldn't reset.
airworx
07-15-2004, 05:47 AM
get the manual for that chiller and find out what it means.
davdjw
07-15-2004, 07:40 AM
Is this a micro tech 200 i was a field tech for them and had the same problem. If its a micro tech 100 then check the current tranformer
chiller32
07-15-2004, 05:03 PM
what is the modle number?
Chillermec
07-15-2004, 10:03 PM
Temporarily jumper the phase monitor control circuit and see if you can clear the alarm. If it does, check setting on the monitor to verify that it agrees with the actual voltage. If you still have a problem, the control contact on the monitor may be suspect.............. several monitors were used, so, I can't be specific regarding the monitor.
in house worker
07-15-2004, 10:24 PM
its a alr35d and the manual says nothing.
salesslime
07-15-2004, 10:31 PM
Where's chillermech when do need him? You're probably having a intermittent bad connection on the MCB board. Clean terminals and re-seat wires in connector.
787 Guy
07-16-2004, 04:50 PM
Its telling you there is a problem with the regulated power supply to the transducers. Theres a test procedure in the IM under troubleshooting power problems
Chillermec
07-17-2004, 08:10 AM
Hey SalesSlime, I believe this is confusing due to the statement..... bad volts ratio is the one you're thinking about. I'm pretty sure the statement is an earlier version of phase/volts