PDA

View Full Version : Solution Sample valve



bertoh
05-17-2010, 03:29 PM
Anyone ever seen a solution sample valve like this on a YIA.
Allthe sample points are the same. Is their a trick to it , or are they plugs like they look and if so whats the best way to get a sample

bullgear420
05-17-2010, 05:53 PM
I believe that you will need a spindle valve tool from York.

bertoh
05-17-2010, 06:30 PM
any chance you have a part num. on it

bertoh
05-17-2010, 06:43 PM
I found it in RP for the unit. Thanks bullgear
any thing I need to know about using it. Is there a check valve in the spindle valve to avoid sucking air into the machine?
TIA

klove
05-17-2010, 10:25 PM
I found it in RP for the unit. Thanks bullgear
any thing I need to know about using it. Is there a check valve in the spindle valve to avoid sucking air into the machine?
TIA

No check valve. Set up as normal and evacuate before opening the valve. May not be necessary all the time, but it's good practice just in case.

bertoh
05-18-2010, 01:36 AM
I have one ordered, and hope it is self explanatory. thanks klove