View Full Version : HW Reclaim Leaker



Blackmira
05-07-2010, 07:40 PM
Got one rack w/ three HW tanks. Not getting any hits but suspecting HW reclaim is leaking. Besides cutting them loose and blowing em up with nitrogen, any secrets/ experience?? Thanks

Phase Loss
05-08-2010, 01:24 AM
pop the pressure relief and stick your sniffer by the drain and hope you can pick up the mixture of water and refrigerant.

Or drain the tank completely of water and leave the drain valve open, refrigerant vapor leaking into the tank will also leave the drain valve.

crackertech
05-08-2010, 08:24 AM
pop the pressure relief and stick your sniffer by the drain and hope you can pick up the mixture of water and refrigerant.

Or drain the tank completely of water and leave the drain valve open, refrigerant vapor leaking into the tank will also leave the drain valve.


Ditto.

icemeister
05-08-2010, 08:44 AM
What's the brand of reclaim tank? I've had Thermastor and Mueller leakers but never had one leaking to the water side.

To my knowledge, both have stainless steel heat exchanger jackets that wrap around the water tank giving you a double wall between the refrigerant and the water. It would then seem very unlikely that you could get a leaker without being able to detect it from the outside.

teddy bear
05-08-2010, 08:55 AM
The only sure way to confirm a refrigerant leak is to isolate the plate from the ref system and pressurize with nitrogen at 300 PSI for several hours. Using electonic leak detectors does not work because of the refrigerant used to blow the foam.
We have never had a refrigerant leak into the water because of the double wall seperating water from the refigerant.
Regards TB

crackertech
05-08-2010, 09:00 AM
Ice it dose not happen often but I had a thermo burst into the water jacket just last year.

mspanky
05-08-2010, 09:22 AM
The last Thermostore I replaced was leaking up through the refrig stubs badly. Looking inside the tank, the interior walls were insulated with what looks like black, rubberized undercoating with only the bottom dome left bare for a heat exchange.

Blackmira
05-08-2010, 11:27 AM
Its a therma. Funny, I got a hit at the hand sink...

Phase Loss
05-08-2010, 11:57 AM
I've seen 3 old therma's do it.

MikeySq
05-08-2010, 06:25 PM
Got one rack w/ three HW tanks. Not getting any hits but suspecting HW reclaim is leaking. Besides cutting them loose and blowing em up with nitrogen, any secrets/ experience?? Thanks

why cut and isolate....... i've found it done before and even tagged that it was done

http://i492.photobucket.com/albums/rr289/MikeySQ/HPIM0158.jpg

roll eyes now
hhaha