05-05-2010, 07:00 PM
I was told by copeland that if you replace one tandem compressor then you must replace both!
What is the reason for this?
thanx
frank
ryan1088
05-05-2010, 07:18 PM
All the people I have talked to that said that were salesmen. I have changed many single compressors in a tandem circuit.
What is the reason for changing the compressor? Burnout? Acid??
supertek65
05-05-2010, 07:35 PM
mid mo
are you from missouri????????????????????????????
I do not think it is a burnout???
that is why I ask
ofcourse any krap from the bad compressor can get in the new one!!!!!!!!!!!!!!!
i remember copeland rep telling me some other reason a few years back but can not remember
ryan1088
05-05-2010, 07:57 PM
Ya I live down at the Lake of the Ozarks and I work down at Fort Leonard Wood.
You do have to be aware of the piping, I know McQuay ended up changing some of the piping of their tandem scrolls from from a 3 pipe to a 2 pipe with a oil crossover. Make sure you end up ordering all the stuff you need.
supertek65
05-05-2010, 08:00 PM
i spent the last year working at ft wood
bct3 barracks!!!!!!!!!!!!!!!!!!!!
weitz/wattz
I am going to just replace both compressors
i just wanted to know what to tell the customers
Ya I live down at the Lake of the Ozarks and I work down at Fort Leonard Wood.
You do have to be aware of the piping, I know McQuay ended up changing some of the piping of their tandem scrolls from from a 3 pipe to a 2 pipe with a oil crossover. Make sure you end up ordering all the stuff you need.
ryan1088
05-05-2010, 08:12 PM
Small world. I hear the funding is in the works to build another BCT.
We were hoping to get some training on those new units over there before we just get a no a/c call on them.
supertek65
05-05-2010, 08:18 PM
i wired up installed started up piped up and commissioned every piece of equipment there!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!
just call me!!!!!!!!!!!!!!!!!!!!!!!!!!!!!1
same with cdc!!!
we are also doing some warehouse soon
frank
Small world. I hear the funding is in the works to build another BCT.
We were hoping to get some training on those new units over there before we just get a no a/c call on them.
traverse tech
05-05-2010, 10:28 PM
we have done it both ways. Never seemed to matter but we changed the oil on the good compressor besides changing out the bad. Both ways we have never had a problem.
Octopus
05-05-2010, 10:37 PM
IN the old days we use to replace both for many reasons, metal shavings, acid, burn out, it can be summed up by the phrase cross contamination. I replaced a trane 3d 15 ton comp in a tandy and one month later the old compressor died and then had to replace old comp that had burnt up and now contaminated the new compressor it's a vicious cycle. We did not loose either new comps after that. In both instances the proper procedure's and precautions were taken to protect the compressors suction line dryers, new oil etc but still if you can why not replace em both it may save you a head ache down the road.
klove
05-06-2010, 08:09 AM
I was told by copeland that if you replace one tandem compressor then you must replace both!
What is the reason for this?
thanx
frank
So that the guy who told you that can take his ol' lady to Maui on their next vacation.............
ryan1088
05-06-2010, 08:10 PM
i wired up installed started up piped up and commissioned every piece of equipment there!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!
just call me!!!!!!!!!!!!!!!!!!!!!!!!!!!!!1
same with cdc!!!
we are also doing some warehouse soon
frank
Sweet, I will take you up on that. Something will happen and of course it'll be 100 outside. Just how things go!
hvac248
05-06-2010, 10:28 PM
The safe bet is to replace both or leave it open to the customer this way.
The compressor went bad for a reason, for which I do not know why, and until I replace it and see what is happening in the system further action may be required.