where exactly in english do you take temp readings for subcooling and superheat in residential fridgs, AC and heat pumps. this site is fantastic

"refer" man that can
11-25-2005, 03:29 PM
To check subcooling you take liquid line temp at the service valve and convert your head to a saturated cond temp.Subtract to get subcooling.