PDA

View Full Version : Trane RTU RTRM board buzz.



lugnut
04-10-2010, 11:47 AM
I don't work on Trane Rtu's, but I have one that I looked at today. I don't have a model number (sorry), but it's a 7 ton unit, about 8 yr old. When I arrived, I found the blower fan starting and running (in econo mode) for several minutes, then the blower drops out for a couple of minutes and the cycle repeats.

Always see solid green led on both econ board and rtrm board, even as I left the job. Put unit into test mode, and first step (blower test) did not energize the blower, (no errors flashes). I though it was a 24 volt short to ground because I got 12 volt readings across the fan contacter coil when the fan contactor dropped out, but despite this, more importantly, I feel the symptom cycle was too well timed to be a random short in the wiring. I did not time the events, but the entire cycle was under 10 minutes, maybe even less. I saw this happen at least 3 or more times.

After 30 min of poking around, the symptoms changed without any cause. I had not changed anything on the unit, then, instead of the blower starting intermittently as described, the rtrm board is making a very loud buzzing noise, from the tall canister part soldered to the board. Still have no alarms or error codes. Had to shut unit off to stop the buzzing. Any one ever heard this buzzing from the rtrm before?

The oa temp was around 57, in case anyone is thinking of a emerg stop due to frost, etc.

Octopus
04-11-2010, 06:46 PM
Model and Ser would sure be nice.... Do you have a picture of this part that is buzzing?

brooklyntech
04-11-2010, 11:37 PM
How do u know its 7 tons with no model? RTRM implies Reiatel; I hink u might have ucp (2x2) board. Get the TRANE manual for UCP controls. It give u everything u need to trouble shoot. By the way u mite have a bad board.

VTP99
04-12-2010, 08:10 AM
How do u know its 7 tons with no model? RTRM implies Reiatel; I hink u might have ucp (2x2) board. Get the TRANE manual for UCP controls. It give u everything u need to trouble shoot. By the way u mite have a bad board.

Does Trane even make a 7 ton unit ?

lugnut
04-13-2010, 03:42 PM
As stated, no model #, no pic, tonnage is estimate. Buzzing is on the RTRM circuit board (board components are integral to the board, not separately replaceable.

Octopus
04-13-2010, 06:42 PM
Did it look like this?

lugnut
04-13-2010, 07:40 PM
It is cylindrical canister, but it about 3" tall.

grandmastad
04-14-2010, 09:21 PM
you got a bad board bud.. replace it..

the sound you are hearing is the micro relay (little black square looking box on the control board).. it will soon crap the bed and yer blower motor will never come on..