View Full Version : McQuay Unit Vent Integration with N2
freddy-b
03-31-2010, 11:09 PM
2-Pipe Chilled Water Cooling and Hot Water Heat-
Software Model UV11 (Valve Control)
Software Model UV12 (F&BP Damper Control)
I have the tables in manual ED-15065-5 that translate the snvts to corresponding N2 points. I have already found discrepencies on several other points and got lucky.
But nviSourceTemp is eluding me. It says it is adf-15 , however it is not. The units have no onboard water sensors ...
Anyone have the correct point address?
TIA
DaveCR
04-01-2010, 11:03 AM
It is possible that the mapping of nvoSourceTemp (adf-47) is accurate. You could watch that point while changing some other adfs.
freddy-b
04-01-2010, 06:28 PM
It is possible that the mapping of nvoSourceTemp (adf-47) is accurate. You could watch that point while changing some other adfs.
47 gives me a static (32) value. If thats it..that proves my nvi value at 15 is not correct...I have also tried several others.
I do not have a nvosourcetemp at any point address on any reference sheet I have. ... What does it say nvisourcetemp is on your list?
Thanks for your help
DaveCR
04-01-2010, 09:25 PM
Here's a link to what I have.
http://www.free-mcquay.com/mcquaybiz/literature/lit_controls/IntegrationInfo/ED15065-5.pdf
This is from page 70.
Source (Water-in) Temp Output
Keypad Menu Path So
This output network variable or read/write BACnet object is used to monitor the source (water-in) temperature. The value of this variable reflects the unit mounted source (water-in) temperature sensor or the value of the source (water-in) temperature input network variable or read/write object. If the input network variable or read/write object is set for a valid value, that value will override the sensor. Otherwise the sensor information will be used.
Good luck with this - our local rep is pretty useless after the sale.
freddy-b
04-03-2010, 09:53 PM
Here's a link to what I have.
http://www.free-mcquay.com/mcquaybiz/literature/lit_controls/IntegrationInfo/ED15065-5.pdf
This is from page 70.
Source (Water-in) Temp Output
Keypad Menu Path So
This output network variable or read/write BACnet object is used to monitor the source (water-in) temperature. The value of this variable reflects the unit mounted source (water-in) temperature sensor or the value of the source (water-in) temperature input network variable or read/write object. If the input network variable or read/write object is set for a valid value, that value will override the sensor. Otherwise the sensor information will be used.
Good luck with this - our local rep is pretty useless after the sale.
I have come to the conclusion that the units are not setup properly for the 2-pipe config.
Powered by vBulletin® Version 4.2.0 Copyright © 2013 vBulletin Solutions, Inc. All rights reserved.