View Full Version : How to determine type of pahse
amustafa
03-30-2010, 02:03 PM
How to detrmine the type of phase connection (single/3-phase) of a unit? what's the quickest way?
printer2
03-30-2010, 02:59 PM
Consult the nameplate?
pdrake65
03-30-2010, 03:30 PM
Consult the nameplate?
:ditto: Looking at the nameplate is the quickest way.
Octopus
03-30-2010, 04:10 PM
If you do not have a name plate the compressor is sometimes the next best thing it will give you voltage phase and capacity.
pecmsg
03-30-2010, 05:01 PM
Wiring Diagram:couch:
Dallas Duster
03-30-2010, 05:05 PM
Lack of capacitors on compressors and motors.
btuhack
03-30-2010, 05:50 PM
Count "hot" conductors in disconnect. Excluding the obvious ground(if), the hot conductors will be switched and/or fused at the disco.
maxster
03-30-2010, 07:51 PM
2 wire is single phase and 3 wire is ....3 phase:eek2: what voltage? always go to ground off each leg from the top 115V its 203/208 single phase on tag...277V to ground it is still called single phase and be 460/480 on tag.3 wires on the top of the disconnect feed in from the pole you read 208/230 between L1-L2-L3 and 115V still to ground.on 460/480 same numbers across between legs and then again 277V to ground
INTECHBILL
03-30-2010, 07:55 PM
How to detrmine the type of phase connection (single/3-phase) of a unit? what's the quickest way?
I think it might be a very good idea to learn how to spell first --- What's pahse >>>?
:couchhide:
jpsmith1cm
03-30-2010, 08:19 PM
If you don't already know.
:callpro:
Not trying to be a jerk, but some of this stuff can get you DEAD.
This guy sure has a lotta questions...lol.