View Full Version : Balanced Port TEV
270wsm
03-27-2010, 09:34 PM
I dont have alot of experience with these valves. When is it better to use a balanced port over the standard valve.
Joe Harper
03-27-2010, 11:18 PM
On condensing units that have fan cycling controls, or areas that have large temperature swings, like a roof top unit. The valve is designed for use where the head pressure has large swings. I put them on everything. It only makes sense....
thefreezerguy
03-28-2010, 01:33 AM
On condensing units that have fan cycling controls, or areas that have large temperature swings, like a roof top unit. The valve is designed for use where the head pressure has large swings. I put them on everything. It only makes sense....
Agreed. I do too. Just about everything I work on has floating head. Like you said, it only makes sense.
270wsm
03-28-2010, 09:51 AM
Well, it looks like I need to start using them then. Like you both have siad, almost everything I work on has some type of head pressure control too. I will try them on a WI cooler install comming up.
thefreezerguy
03-29-2010, 11:24 AM
Well, it looks like I need to start using them then. Like you both have siad, almost everything I work on has some type of head pressure control too. I will try them on a WI cooler install comming up.
Ask your local wholesaler for Sporlan TEV literature for standard and balanced port valves. Then look at how the pressure differences across a standard valve affects its capacity. It will then make sense to you why to use a balanced port valve when the head pressure fluctuates.
Joe Harper
03-30-2010, 07:29 PM
Ask your local wholesaler for Sporlan TEV literature for standard and balanced port valves. Then look at how the pressure differences across a standard valve affects its capacity. It will then make sense to you why to use a balanced port valve when the head pressure fluctuates.
If you keep using facts, and logic you are going to start a flame war around here..better watch it.... :grin2:
thefreezerguy
03-30-2010, 07:35 PM
If you keep using facts, and logic you are going to start a flame war around here..better watch it.... :grin2:
Got it!:LOL:
Super Tech JJ
04-12-2010, 06:10 PM
Something to be cautious about with TEV versus cap tube, orifice or some other fixed restriction metering. If you install a TEV from the other pressure drop device you will need to add hard start if your compressor is piston and valve.(with single phase power) The expansion valve will close once the compressor stops and the compressor won't want to start again without a start relay and capacitor. Three phase compressors and scrolls will start fine.
GT Jets
04-12-2010, 06:24 PM
Really the only time to use an internally equalized valve would be when there is very little pressure differential across your evaporator. Otherwise externally will almost always be the valve of choice...
A perfect example of a low diff. coil would be a tube type heat exchanger in a process chiller with no distributor, or a tempering coil in an AC unit...
Another thought about the retrofit from cap to Valve, the charging method will be completely different, cap=superheat/OSA and valve=subcooling...it will normally take a tad more gas to get a valve to work where a cap tube once was...:.02:
GT
Boise500
08-09-2010, 06:24 PM
Sometimes a balanced port valve can be a little to responsive, if it hunts, add a layer of electrical tape between the bulb and the suction line. After you rule the normal causes out.
Joe Harper
08-09-2010, 10:29 PM
If it hunts, you need to finish adjusting it...not hack it...
thefreezerguy
08-09-2010, 11:19 PM
Sometimes a balanced port valve can be a little to responsive, if it hunts, add a layer of electrical tape between the bulb and the suction line. After you rule the normal causes out.
I don't think so.........
Joe Harper
08-10-2010, 09:33 PM
Hehe...run cap bandit moves on to txv's.....
pherman
08-11-2010, 12:07 AM
:eek2:
Sometimes a balanced port valve can be a little to responsive, if it hunts, add a layer of electrical tape between the bulb and the suction line. After you rule the normal causes out.
:eek2:
FridgeMagnet
08-11-2010, 01:56 AM
I have to agree with the preveous posts - alway better to use balanced port txvs. the only time I don't is when I have a freezer to deal with the load after defrost use a mop valve. The thing about the tape is that your introducing another element to the system - better to put in the time even though it is a pain. Once it's set ur done forever or at least till warranty is over - lol