03-14-2010, 01:11 PM
What is the normally accepted range Delta T between supply & return on the heating side of a heat pump system? My new system was giving about 22F degrees when it was low 50's outside ambient, but barley gives a max delta of 10F when its low 40's outside. Thanks!
pacnw
03-14-2010, 01:37 PM
.
ACFIXR
03-14-2010, 02:16 PM
switch the fan to auto and system to heat:yes:
BaldLoonie
03-14-2010, 03:42 PM
Sounds very low. Typical 20+ at 30 out, close to 30 degree rise at 50 out with proper airflow.
beavercreekhc
03-14-2010, 08:50 PM
with a bryant h/p and an electric air handler with no heat strips running i was getting a 32 degree F split with a 20 degree F temp. outside
Gimmered
03-14-2010, 10:37 PM
My Nordyne will give me 20.3° at 17°.
chuckcrj
03-14-2010, 11:18 PM
Sounds very low. Typical 20+ at 30 out, close to 30 degree rise at 50 out with proper airflow.
See the key words; Proper Airflow.
Paul12644
03-15-2010, 12:07 AM
I had a new Lennox G71MPP furnace and XP14-042 heat pump installed a month or so ago. The Delta T at 55 degrees exterior temperature with the heat pump running was 40.
crmont
03-15-2010, 12:40 AM
What is the normally accepted range Delta T between supply & return on the heating side of a heat pump system? My new system was giving about 22F degrees when it was low 50's outside ambient, but barley gives a max delta of 10F when its low 40's outside. Thanks!
Call 'em back!
What's you model numbers?
gary_g
03-15-2010, 08:17 AM
What is the normally accepted range Delta T between supply & return on the heating side of a heat pump system? My new system was giving about 22F degrees when it was low 50's outside ambient, but barley gives a max delta of 10F when its low 40's outside. Thanks!
Tech Operating Data for my 3-ton, 14 SEER, 9 HSPF pump:
Ambient-------Temp after indoor coil
Temp-------(based on 70F return air temp)
60F---------------105.8F
50F---------------101.5
40F---------------97.1
30F---------------93.4
20F---------------89.9
10F---------------86.2
0F----------------82.6
Take care.
pacnw
03-15-2010, 09:24 PM
Tech Operating Data for my 3-ton, 14 SEER, 9 HSPF pump:
Ambient-------Temp after indoor coilambient usually refers to outdoor temp unless otherwise specified
Temp-------(based on 70F return air temp)
60F---------------105.8F
50F---------------101.5
40F---------------97.1
30F---------------93.4
20F---------------89.9
10F---------------86.2
0F----------------82.6
if I were to read CAREFULLY you are saying that, for example, an ambient(outdoor) temp of 0*F with a return air temp of 70* gives you a supply temp of 82.6*F or 12.6* temp rise/delta T
Take care..
gary_g
03-16-2010, 07:34 AM
.
You are reading the columns incorrectly.
Ambient temps are in the column going from 60F to 0F, with the corresponding coil temp in the column next to each ambient temp.