I'm wondering if any signal is sent through the W2 terminal from a Honeywell 2 stage thermostat when the thermostat is setup as a 1 stage thermostat for a 1 stage furnace.
beenthere
03-14-2010, 12:08 PM
No, or you wouldn't have to tell it that it is controlling a 2 stage furnace when its hooked to a 2 stage furnace.
john_ertw
03-14-2010, 12:59 PM
No, or you wouldn't have to tell it that it is controlling a 2 stage furnace when its hooked to a 2 stage furnace.
I guess if the thermostat is set as 1 stage all calls for heat are through W1 then.
Thanks.
bzzline
03-15-2010, 10:09 PM
I guess if you told the tstat it was controling a heat pump you would not get 24volts to w1 in stage 1 .
big sky hvac
03-15-2010, 10:14 PM
I can't say about other brands of t-stat's, but honeywell's multi-stage t-stat's come set up as a single stage. If you have a multi-stage furnace or a heat pump, you would actually have to go into the installer set-up to change it to multi-stage. Don't know if that helps you at all, just an fyi.