controlstec
02-12-2010, 02:21 PM
I am working on a site that has had problems with communication between Tridium R2 and Delta 3.30. There are two things happening, one, the Delta controllers have been dropping offline on a consistent basis for about 3 years now. The solution provided to me from Delta for this particular problem has varied and I've tried all of them, but none has been totally successful. The second thing that has been happening is that the Tridium Jaces have been locking up. The Jaces stop polling data from the Delta controllers and therefore none of the data from the Delta controllers is read at the Jace or the Front End graphics. The only way to get communication between the two systems going again is by cycling power to the Jace. In the standard output of the Jaces, I get the following error for just about all the controllers onsite:
WARNING: BACnet Read Property Multiple Error: presentValue [/AJJC_Support/BACnetTemp/Alameda_Reheat_VAV_A3_6R]
WARNING: BACnet Read Property Multiple Error: statusFlags [/AJJC_Support/BACnetTemp/Alameda_Reheat_VAV_A3_6R]
WARNING: BACnet Read Property Multiple Error: priorityArray [/AJJC_Support/BACnetTemp/Alameda_Reheat_VAV_A3_6R]
WARNING: BACnet Read Property Multiple Error: presentValue [/AJJC_Support/BACnetTemp/Alameda_Reheat_VAV_A3_7R]
WARNING: BACnet Read Property Multiple Error: statusFlags [/AJJC_Support/BACnetTemp/Alameda_Reheat_VAV_A3_7R]
WARNING: BACnet Read Property Multiple Error: priorityArray [/AJJC_Support/BACnetTemp/Alameda_Reheat_VAV_A3_7R]
I have been in contact with Tridium support and they tell me that the Jaces are trying to communicate to the Delta controllers using the read property multiple type of BACnet message and they don't support read property multiple. They recommend I set the ReadPropertyMultiple value on each of the Delta controllers to false.
My questions are, why are the Delta controllers still dropping offline and is the assessment of the ReadPropertyMultiple function the actual cause for the Delta/Tridium communication problems and if that is the problem, what is the fix? Can the ReadPropertyMultiple function be set to false in the Delta controllers?
WARNING: BACnet Read Property Multiple Error: presentValue [/AJJC_Support/BACnetTemp/Alameda_Reheat_VAV_A3_6R]
WARNING: BACnet Read Property Multiple Error: statusFlags [/AJJC_Support/BACnetTemp/Alameda_Reheat_VAV_A3_6R]
WARNING: BACnet Read Property Multiple Error: priorityArray [/AJJC_Support/BACnetTemp/Alameda_Reheat_VAV_A3_6R]
WARNING: BACnet Read Property Multiple Error: presentValue [/AJJC_Support/BACnetTemp/Alameda_Reheat_VAV_A3_7R]
WARNING: BACnet Read Property Multiple Error: statusFlags [/AJJC_Support/BACnetTemp/Alameda_Reheat_VAV_A3_7R]
WARNING: BACnet Read Property Multiple Error: priorityArray [/AJJC_Support/BACnetTemp/Alameda_Reheat_VAV_A3_7R]
I have been in contact with Tridium support and they tell me that the Jaces are trying to communicate to the Delta controllers using the read property multiple type of BACnet message and they don't support read property multiple. They recommend I set the ReadPropertyMultiple value on each of the Delta controllers to false.
My questions are, why are the Delta controllers still dropping offline and is the assessment of the ReadPropertyMultiple function the actual cause for the Delta/Tridium communication problems and if that is the problem, what is the fix? Can the ReadPropertyMultiple function be set to false in the Delta controllers?