cmakowk
01-26-2010, 10:11 PM
I have a Trane Summit ver.17
that has Comm3 and Comm5 devices.
Comm 3 devices are reading fine.
The Comm5 devices are lon and were reading except
for a lon fieldserver, which translated AAon units to lon.
I added another lon fieldserver for another AAon unit
and now the all the lon devices are offline.
During this process, I hit something on the workstation
that added all the SCC lon devices in the drop down tree
even though the existing graphics showed them already.
So when you click it on these added items it would bring up that controller.
I connected Rover on the trunk and discovered all the devices
and am able to see all the controller I/Os
but the BCU shows everything offline.
On the workstation, I performed a scan and it will see all the
controllers and NIDs but no data on the graphics or if I edit
the controller I get all ???
Any ideas?
that has Comm3 and Comm5 devices.
Comm 3 devices are reading fine.
The Comm5 devices are lon and were reading except
for a lon fieldserver, which translated AAon units to lon.
I added another lon fieldserver for another AAon unit
and now the all the lon devices are offline.
During this process, I hit something on the workstation
that added all the SCC lon devices in the drop down tree
even though the existing graphics showed them already.
So when you click it on these added items it would bring up that controller.
I connected Rover on the trunk and discovered all the devices
and am able to see all the controller I/Os
but the BCU shows everything offline.
On the workstation, I performed a scan and it will see all the
controllers and NIDs but no data on the graphics or if I edit
the controller I get all ???
Any ideas?