01-26-2010, 12:24 PM
How many CFM's of air equal one ton of refrigeration?

chillerguy81
01-26-2010, 12:53 PM
That all depends on how the system is engineered. Engineers normally figure 350 - 400 cfm per ton.

LocoMike
01-27-2010, 10:00 AM
The answer will vary depending on application. Rule of thumb is 400 CFM/Ton for a residential unit or unti with very little outdoor air.

Rule of thumb for 100% outdoor air is 250 CFM/Ton.

Big difference.

brooklyntech
01-27-2010, 10:42 AM
250-400-600 cfm- different variables require different cfms

Mikeymoe
01-24-2011, 09:35 AM
what is the basis of your question? all posters are correct, but it depends on type of system, static pressure, etc.

makinmoney
01-24-2011, 10:22 AM
Liebert CRAC systems go about 700 cfm's per ton......it depends on the application and the Manfacturer's engineering of the system.

Serviceyourac
01-24-2011, 10:39 AM
Yeah, there is no real "direct" answer for this question. There are only rules of thumb for estimations.

flange
01-24-2011, 03:16 PM
btuh=1.08xcfmxdelta t

12000=1.08x400x27.78

1 ton=1.08x desired airflowx desired delta t

This is for illustration only, and does not reflect actual calculations since it does not compensate for both latent and sensible loads.