illuzionb18c1
01-19-2010, 02:19 PM
Minisplit:
Total cooling capacity: 36000 btu/h
Fan airflow (L/M/H): 883/988/1060 cfm
1) given the information above, will this unit only have max cooling of 36000 btu/h at HIGH airflow of 1060 cfm? If so, how do I calculate how much cooling I will get with Low/Medium fan settings?
2) Assuming airflow of 1060 cfm and sensible heat ratio of .81 (therefore 29160 btu/h of sensible btu/h), if my room temperature is 75F db, does that mean I could technically get 50F db off my coil (see calculation below)?
29160 btu/h = (1060 cfm) * (1.1) * (75-X) where X=50F
3) How can I find out how cold the Leaving air temperature can be off an evaporator if i know the sensible capacity?
thanks in advance
Total cooling capacity: 36000 btu/h
Fan airflow (L/M/H): 883/988/1060 cfm
1) given the information above, will this unit only have max cooling of 36000 btu/h at HIGH airflow of 1060 cfm? If so, how do I calculate how much cooling I will get with Low/Medium fan settings?
2) Assuming airflow of 1060 cfm and sensible heat ratio of .81 (therefore 29160 btu/h of sensible btu/h), if my room temperature is 75F db, does that mean I could technically get 50F db off my coil (see calculation below)?
29160 btu/h = (1060 cfm) * (1.1) * (75-X) where X=50F
3) How can I find out how cold the Leaving air temperature can be off an evaporator if i know the sensible capacity?
thanks in advance