PDA

View Full Version : Is there a 24v tstat for hot yoga?



mogy
01-12-2010, 11:58 PM
I've taken a Hot yoga studio on and I need a thermostat with high heat settings and fan on/auto. Long story short I need the fan settings so I can turn fan on to allow fresh air to purge the room and when they need the heat I need it to be 105. I have an outdoor furnace w/o cooling. I was advised by the manufacturer to not use line voltage stat, but a 24v. My tstat rep says I won't find a stat that goes over 90. Has anyone got any suggestions? Or am I stuck with 120v?

icemeister
01-13-2010, 07:08 AM
Check this out:
http://cgproducts.johnsoncontrols.com/MET_PDF/125188.PDF

mogy
01-13-2010, 08:07 AM
I like it & it's similiar to what we would have used, but no fan on/auto :(

kontrolsfreek
01-13-2010, 09:29 AM
We have worked with a couple of these hot yoga studios and found that the Honeywell T775 universal controller work great. It can be powered 24v and it allows you to set the temp to 105 or 110.