View Full Version : Chiller Flow Switch
lowtech
01-01-2010, 06:39 PM
Can anyone help me with a Manufacturer and Model Number on a differential pressure flow switch to replace the old paddle style?
I will be using them on some Carrier 30gtn 150 to 200 ton chillers.
chillerguy81
01-01-2010, 06:44 PM
You / we will need to know the pressure range your dealing with. I normally see the controls made by Johnson or Honeywell, I'm sure there are others as well.
mustardman
01-01-2010, 07:01 PM
Can anyone help me with a Manufacturer and Model Number on a differential pressure flow switch to replace the old paddle style?
I will be using them on some Carrier 30gtn 150 to 200 ton chillers.
Go to ifm website I have used them quite a bit lately a bit pricey but seem to hold up well
chillrdude
01-01-2010, 07:34 PM
I have used these from Midwest before, very nice kinda pricey though.
http://www.midwestinstrument.com/diaphragm/140.asp
glennwith2ns
01-01-2010, 07:58 PM
veris , have GOOD luck with these
http://www.veris.com/product_results.aspx?category_guid=163eace4-575f-4d8b-bd04-6b186c0d1a2e
lowtech
01-01-2010, 07:58 PM
Those chiller barrels see about a 5 psi delta at 400 gpm.
I'll have to call and see if Midwest or ifm has a range a little lower than 25 psi. I like to run in the middle of the range but it might work anyway.
york56
01-02-2010, 08:50 AM
Here is a link look up pressure switch then differential pressure switch there is one there with 0-10 psid http://www.mcmaster.com/#
klove
01-02-2010, 10:56 AM
Custom Control Sensors, Midwest Instruments, Orange Research. In your particular case I would opt for Orange Research because of the low delta P. You'll have to get in touch with them and tell them the specifics of the instrument you want because they have very little if any off the shelf devices. I'd have it calibrated in feet of H2O rather than psi. That will give you a higher control point and wider operating range than psi.
May also want to consider thermal type flow sensor.
Airmechanical
01-02-2010, 12:17 PM
whats wrong with the paddle?
.
always looking
01-02-2010, 11:26 PM
If you would like a good alternative to McDonald Miller or Johnson take a look at a Harwil Q5. We used them on larger chillers, designed for more flow than the other manufactures can handle.