I really need some furnace sizing help so I can make a decision.
Current Setup:
1920's three storey semidetatched house in Toronto, double brick almost no insulation.
Approximately 2200sqft (including basement)
20year old Lennox G8 furnace 120,000BTU (90,000 BTU @75% eff)
I've performed two separate heat loss calculations (one using HVAC Calc) and the other using a simplified example of the Canadian CSA F280.
HVAC Calculation Report = 105,000BTU
F280 Simplified Calc = 80,000BTU (takes into account 40% oversize)
I am looking at the Carrier Infinity 96% HEF. The problem is it comes in an 80,000BTU and an 100,000BTU version. And I don't know which one I should choose.
My understanding the way the 2-stage variable speed Carrier Infinity works means a 100,000BTU would not be a problem even if it might be a little to big, due to the variable speed.
Some input would be greatly appreciated so I can pick a model and move on. I plan to pair this with a 2-TON condenser.
Thanks
Detox
Current Setup:
1920's three storey semidetatched house in Toronto, double brick almost no insulation.
Approximately 2200sqft (including basement)
20year old Lennox G8 furnace 120,000BTU (90,000 BTU @75% eff)
I've performed two separate heat loss calculations (one using HVAC Calc) and the other using a simplified example of the Canadian CSA F280.
HVAC Calculation Report = 105,000BTU
F280 Simplified Calc = 80,000BTU (takes into account 40% oversize)
I am looking at the Carrier Infinity 96% HEF. The problem is it comes in an 80,000BTU and an 100,000BTU version. And I don't know which one I should choose.
My understanding the way the 2-stage variable speed Carrier Infinity works means a 100,000BTU would not be a problem even if it might be a little to big, due to the variable speed.
Some input would be greatly appreciated so I can pick a model and move on. I plan to pair this with a 2-TON condenser.
Thanks