View Full Version : 5 ton ac
service call was unit not cool, (but the house is cool not enough but it is cool), unit runs all day and night, never turns off.
set gauges low of r22, cut coil and washed coil, coil dirty.
soldered coil back to unit, opened valves done, so i thought got a call back still doing the same thing.
ruud unit
md#uamb-060jaz
split system
subcool
psi-250
temp-118 liquid line temp @ evap coil-27.5
superheat
psi-64
temp-35
suctionline temp-73 (6-8 from compressor).
any ideas guys really need the help thanks.
BaldLoonie
08-06-2009, 02:57 PM
We'll be glad to help - but: need to get yourself promoted to professional member so we can move this thread behind closed doors. Site rules don't allow technical discussion here. You need 15 posts, so post a few more, try general or food maybe :p and apply for your pro membership.
thanks will do, 15 not a bad number.
smurry
08-06-2009, 05:12 PM
I'm in the same boat...13 to go (12 if you count responding to my own thread, not sure if that counts).
beenthere
08-06-2009, 05:27 PM
I'm in the same boat...13 to go (12 if you count responding to my own thread, not sure if that counts).
It counts.
mchild
08-06-2009, 05:51 PM
I'm in the same boat...13 to go (12 if you count responding to my own thread, not sure if that counts).
What time is it there in Houston? (this should make you at 15)
guys in a world of hurt thinking its the txv, but would like to hear your opinions as well thanks.
udarrell
08-07-2009, 05:07 PM
service call was unit not cool, (but the house is cool not enough but it is cool), unit runs all day and night, never turns off.
set gauges low of r22, cut coil and washed coil, coil dirty.
soldered coil back to unit, opened valves done, so i thought got a call back still doing the same thing.
ruud unit
md#uamb-060jaz
split system
subcool
psi-250
temp-118 liquid line temp @ evap coil-27.5
superheat
psi-64 is SLT 73 -37-SST = huge 36-F Superheat
temp-35> 64-psig is 37-F
suctionline temp-73 (6-8 from compressor).
any ideas guys really need the help thanks.
Well, 36-F is a lot of superheat, also there is no Subcooling, therefore there's either not enough liquid refrigerant entering the coil or you have a huge hot air leak into the Return-Air system.
Could be a combination of both, hot air source leaking into the Return & low on R-22. Just a guess... ;) :p - Darrell
thanks bud will check, and will keep you guys posted.
udarrell
08-09-2009, 12:44 PM
thanks bud will check, and will keep you guys posted.
Also, data indicative of low charge, & several other problems.
docholiday
08-09-2009, 09:48 PM
condesner (low subcooling) - not enough charge
evaporator - (high superheat) not enough charge
Where is it? Cant be hiding somewhere else.
37 degree coil doesnt suggest a huge load on the system. Although I am confused how you measured 27 at the evaporator?