OK. Here we go.
One of my stores is having trouble with a couple Hussmann NF6 cases (Impact type open high back cases). I haven't been there yet, but I will, SOON, I'm sure.
Here is what I know.
Honeycombs have been cleaned, HG defrost checks out (3x daily, 12 minutes, 15 runoff, 60 termination)
Complaint is that there is ice building in the honeycombs.
Humidity is "good". Nobody gave me specific readings like I asked for.
Thought? Suggestions?
Thanks.
shaun66
07-28-2009, 12:59 PM
OK. Here we go.
One of my stores is having trouble with a couple Hussmann NF6 cases (Impact type open high back cases). I haven't been there yet, but I will, SOON, I'm sure.
Here is what I know.
Honeycombs have been cleaned, HG defrost checks out (3x daily, 12 minutes, 15 runoff, 60 termination)
Complaint is that there is ice building in the honeycombs.
Humidity is "good". Nobody gave me specific readings like I asked for.
Thought? Suggestions?
Thanks.
rip them out, install doors
jpsmith1cm
07-28-2009, 03:08 PM
You buying?
cold spell
07-28-2009, 07:22 PM
I believe those cases have anti sweat heaters in the primary honeycombs. Could be that.
jpsmith1cm
08-21-2009, 10:19 AM
Some resolution to the problems.
Yes, I finally got there, as predicted.
Humidity in store was not "good" as I was told. Store was cold and humid. A dose of heat reclaim dried that out pretty nicely. Store is actually comfortable now.
Also, hot gas differential was only about 10 psid. Crank that to 20 for a better flow through defrost.
Now for the tricky one. Out of 25 circuits, 2 were overlapping hot gas defrost. Want to guess what one of them was?
Phase Loss
08-21-2009, 11:45 PM
CU23
could it be the cases in question?toe tap2
jpsmith1cm
08-21-2009, 11:47 PM
CU23
could it be the cases in question?toe tap2
cheers1
You got it.
det1
Hot gas defrost doesn't much care for overlapping defrosts.