View Full Version : Opinion on recent service/quote
vanenk
07-27-2009, 05:43 PM
Hello,
Just a home owner, have enjoyed reading many posts on this site. Would like some professional opinions on work I had done on my unit today.
Here's the scenario: Home purchased in last year w/ 5 ton heat pump (~13 yrs old, b/u electric heat) quit blowing cold air this past Friday. Called home warranty co., they send out a local technician. Tech states low refrigerant, and refills. When asked how many pounds needed to be added, he says, "Quite a few." He says they don't normally leak test on first visit, but it was "real low." When questioned again about quantity of added refrigerant, he says, "Well, we don't really measure in pounds, there's a mathematical formula for figuring up how much we use." At then says, "How much does this unit hold?" He looks at decal on side of unit and says "16 pounds! Wow! I think I probably added 8-9 pounds." I knew how much the unit held from seeing the decal before. He takes out a small "sniffer" and uses it around the coils of the outside unit, and says the whole unit (inside/out) will need to be replaced because it is leaking.
Now, the warranty specifies it's all covered for a fixed fee, no big deal. Here's what I am curious about:
1) Is it difficult to determine how much refrigerant was added? I realize he needed to know capacity first, I just thought he would be able to tell (or would want to keep track for billing the warranty co.) of how much was added.
2) Is using a sniffer device the "best" or "professional" way to assess leakage? Would testing pressure/vacuum be more precise?"
I realize on these warranty jobs, reimbursement might be slim, so they try to keep their expenses to a minimum. My guess is the warranty co. will send another local hvac co. out for a second opinion before agreeing to shell out ~$Removed Pricing. It would be nice to get a new unit for next to nothing, but I just want the proper correction, whether it's repair or replace. This leads me to my final question:
3) What questions do I need to ask if repair is determined the proper route? What if replacement is authorized?
It's not that I don't trust anybody, but I do live by the "Buyer Beware" belief. I've read some really good posts on this site about doing the right thing, and I believe most people live by that rule. I want to make sure I know the right questions to ask. I look forward to hearing from you all.
Thanks!:)
bwalley
07-27-2009, 06:10 PM
1) To know how much refrigerant was added, the tech. should have used a scale, then he would know exactly how much refrigerant was added.
2) It depends on the refrigerant, if it was R22, a sniffer is fine, there are also other methods as well.
3) The Home Warranty company is going to do everything they can to avoid paying to install a new unit, it isn't up to you what route they go, unless you decide to pay for the new unit.
beenthere
07-27-2009, 06:16 PM
He should have used a scale. Its the only way to know how much was put in.
Using a sniffer is fine. He probably doesn't know how to use it right.
Using a vacuum, would only tell thet there is a leak, it wouldn't help fined it.
If your unit needs replaced.
Use another company.
A scale is the only way to tell how much refrigerant is used.
Home warranty companies i have delt with will do everything to string you along till the warranty expires. Yours may be different.
HVAC Pro
07-27-2009, 06:47 PM
Amazing isn't it? Scales certified by the federal government is required for selling hamburger, but not for refrigerant that sells for 10-20 times the per pound cost.
I use a digital scale anytime refrigerant goes into or is removed from a system.
For the most part, I stopped reading after I saw "home warranty company".
vanenk
07-27-2009, 07:55 PM
For starters, I appreciate everyone's input regarding refrigerant measurement. OK, it appears the prevailing opinion regarding home warranty cos is very low. Understandable, I work in the health care industry and I've dealt enough with health insurance cos to know the routine. GENERALLY speaking, are the HVAC service cos that partner with home warranty cos reputable and well trained? Probably few and far in between?
If my unit is truly in need of replacing rather than repair, I may decide to bypass the warranty company and go out of pocket with a company of my own choice, versus one picked for me. My concern is the quality/experience of the installers. Free/low cost today=small fortune tomorrow if it's not done right.
Any other thoughts or comments would be appreciated greatly.
Thanks for your input!
bwalley
07-27-2009, 08:03 PM
For starters, I appreciate everyone's input regarding refrigerant measurement. OK, it appears the prevailing opinion regarding home warranty cos is very low. Understandable, I work in the health care industry and I've dealt enough with health insurance cos to know the routine. GENERALLY speaking, are the HVAC service cos that partner with home warranty cos reputable and well trained? Probably few and far in between?
If my unit is truly in need of replacing rather than repair, I may decide to bypass the warranty company and go out of pocket with a company of my own choice, versus one picked for me. My concern is the quality/experience of the installers. Free/low cost today=small fortune tomorrow if it's not done right.
Any other thoughts or comments would be appreciated greatly.
Thanks for your input!
Just because an A/C company is doing work for a home warranty company, does not mean they are not a good contractor.
A home warranty company is an insurance company that pays contractors to repair the equipment they cover and it is the warranty company that tells the contractor what it will pay for and how much they will pay.
Pretty much the same thing as any other insurance company.
Just becaus a Dr. works for an insurance company, does not mean they are a bad dr. does it?.
2old2rock
07-27-2009, 10:07 PM
We do home warranty work. Most around here don't. I don't really like the calls, because it's another layer of bs to get things running right. That being said, we treat them just like any other call. And we always use a scale to know how much to charge a customer for refrigerant. How else would he know what to charge? And when we see a large amount needed, we look for a leak untill we find it. And 16 lbs in a 5 unit seems a bit fishy.
Just becaus a Dr. works for an insurance company, does not mean they are a bad dr. does it?.
It don't mean the doctors bad but insurance companies limit what can be done.
DanW13
07-27-2009, 10:34 PM
You would think everyone would use a scale when charging a Condenser, if they do it without a scale they maybe the one who loses out by not knowing how much they used ? So it would be to everyone's benefit to use a scale IMO....
mark beiser
07-27-2009, 10:54 PM
It would be nice to get a new unit for next to nothing
Flip your home warranty contract over and read everything in the "Limitations of Liability" section.
Within that section can be found thousands of dollars worth of non covered items when it comes to a home warranty company replacing the system.
You are usually better off taking whatever pittance they will give as a cash out, and finding a contractor you are comfortable with yourself.
nick muniz
07-27-2009, 11:08 PM
Around here the the contractors that are used by the warranty companies are the bottom of the barrel that have burned their bridges with the general public. Duct tape and bailing wire are their prefered method of repair and they don't usually own a scale.
That amount of refrigerant would probably be used on a commercial unit.
git-r-dun
07-28-2009, 12:07 AM
Just becaus a Dr. works for an insurance company, does not mean they are a bad dr. does it?.
It don't mean the doctors bad but insurance companies limit what can be done.
That is a correct statement. They do limit what can be done and unfortunately HVAC companies, even the good ones, do have to compromise quality for quantity at times. So it's like a management company on a cheap budget. This is why the perception (and reality in a lot of cases) of "bad" companies come from. I wouldn't necessary call them bad, but maybe inexperienced as the majority companies will have a low payroll in order to compensate for some profit. My opinion and experience with this matter ofcourse.
vanenk
07-28-2009, 06:27 AM
Thanks for all the replies. I know the warranty co will be sending another co out for a second opinion, and more than likely they will find a repair solution--which is fine with me, as long as it is a real fix, but I'm realistic enough to know it will probably last until the warranty period expires:p.
If replacement is the determined remedy, I would rather take the cash settlement and go with a company (and equipment!) of my choosing.
I was not trying to impugn the reputations of cos that do home warranty work, but 2old, nick, and git-r verbalized what my concern was: More reputable HVAC companies will not allow their standards to be compromised by a warranty co., so they don't partner with them. The red tape and reimbursement issues can result in decreased revenue, which requires a lower operating budget, and therefore quality of workforce and materials must be constrained. I'm not complaining, I realize that's the way of the world. I just want to be aware, so I can make the best decision. I would rather spend more and get it done right--It always costs less to do things right the first time.
Again, thanks for the insight, I'll keep everyone posted on the continuing saga...
bdw293
07-28-2009, 10:26 PM
The company I work for does work for a Home Warranty company. If it is over 3 lbs we leak check. If less we are told not to. On the first visit. Second visit it gets checked. When I do add 3 or less I check the service valves and schraders on first call. When we replace systems we treat it just like a cash customer. Home warranty just provides the equipment ( they use a carrier product). The problem I see is they try to bully us into using mismatched equipment. Say installing a 13 seer heatpump on 10 seer Airhandler. We refuse to do the work that way. Chances are slim you'll get a new system out of them, but it does happen. If their contractor does replace your unit make sure they pull permits and it gets inspected if applicable in your area.
junkhound
07-28-2009, 10:46 PM
we don't really measure in pounds, there's a mathematical formula for figuring up how much we use
First a disclaimer that I do not do any residential work, except gratis for friends and neighbors. However, in the industrial/aerospace world, do work with a lot of engineers, VERY rarely will anyone (usually a new college grad) spout out that 'formula' line. Everybody in on the discussion immediately knows that person is a big BS artist who does not know what they are doing.
Just a comment. <G>
fishnfool
07-28-2009, 11:07 PM
Thanks for all the replies. I know the warranty co will be sending another co out for a second opinion, and more than likely they will find a repair solution--which is fine with me, as long as it is a real fix, but I'm realistic enough to know it will probably last until the warranty period expires:p.
If replacement is the determined remedy, I would rather take the cash settlement and go with a company (and equipment!) of my choosing.
I was not trying to impugn the reputations of cos that do home warranty work, but 2old, nick, and git-r verbalized what my concern was: More reputable HVAC companies will not allow their standards to be compromised by a warranty co., so they don't partner with them. The red tape and reimbursement issues can result in decreased revenue, which requires a lower operating budget, and therefore quality of workforce and materials must be constrained. I'm not complaining, I realize that's the way of the world. I just want to be aware, so I can make the best decision. I would rather spend more and get it done right--It always costs less to do things right the first time.
Again, thanks for the insight, I'll keep everyone posted on the continuing saga...
I wish all Hvac companies and homeowners understood this! Not saying all that work for these home warranty co. are bad but around here I haven't seen the good ones yet!
vanenk
07-29-2009, 02:10 PM
UPDATE: The home warranty co has authorized replacment of the outdoor unit and air handler. I plan on taking the cash settlement, so I have called a few local cos with good reputations for estimates, since I want to upgrade to a more efficient unit, plus I want to be the end customer, not the warranty co.
I am interested in hearing opinion on brands, I know that can be like the old GM/Ford/Dodge argument, so I would appreciate any substantive info (i.e., warranty, actual performance versus stated performance, etc.), as well as thoughts regarding single/two stage units, and any other thoughts pertinent. As a non-professional, I try to inform myself, but I won't be offended with any info you provide. Assume I know very little--compared to you all, I do!
Here is my scenario:
--3200 sq ft (single story w/ conditioned bonus room over garage)
--Currently 5-ton, 11.5 SEER Bryant unit w/ b/u elec heat strips (in all electric area); the unit is ~14 yrs old, and has kept the house comfortable. Cooling bill for summer ~100/month for 3 months, heating bill ~150-200/month for 4 months (may have more to do w/ bumping up stat too quick, and heat strips kicking in immediately- this is the first time we've had a heat pump)
--Air handler and ductwork in attic- the cos have informed me the ductwork appears great, and I have adequate return (1440 sq in= 2 sq ft per ton); had duct leak testing done earlier this year- ~22% leakage- I am looking to get this sealed.
Based on my initial research, I am looking at same size unit, leaning towards a 15-16 SEER unit, anything higher would have a much longer ROI--we plan on staying here 10-12 years.
Reps have told me w/ a 5-ton unit it is almost impossible to meet the standards for the 30% federal tax credit.:( Apparently Carrier doesn't have one. One rep says Trane has one in the 15-16 SEER range.
I know alot of you are going to ask about manual J, so I will say this- neither rep has mentioned anything about it, however one rep mentioned he's looked at the walls and window location/type, and asked about how well the current unit has kept us comfortable, so he's given some indication(?) regarding it. Here's my take: No one is going to do an actual manual J until I agree to buy from them. So, I won't know price until I know size, I can't know size until I know manual J, I can't know manual J until I agree to price, which I don't know. I could get a quotes for a slightly smaller, same size, and slightly larger units, and then have them make their calculation, but my guess is it would come out no smaller than what I have, and perhaps even larger. My other concern is the variability in manual J- in other words, the assessment is only as good as the person who does it. I did a spreadsheet assessment (I know, not the real thing) from www.fast-calc.com, and the figures came in just over 4 tons. Add 20%, looking at 5 tons. And the unit I have is keeping me comfortable, and my electric bills are very reasonable, based on what the utility co and both reps have told me.
SO...what are everyone's thoughts? I know, a lot of info here, but I bet you guys can pick thru it quickly. Again, I want to do this right the first time, so I am trying to make as informed a decision as I can. Thanks for all your help!:)
bdw293
07-29-2009, 06:44 PM
First off with 3200 sq ft you do not want to go smaller. You can't go larger than a 5 ton unless you have 3 phase power or you would have to use 2 seprate units. Our company installs American standard (Trane) and we have had good luck. I would go 5 ton 14 or 15 seer R410A single stage compressor with a varible speed blower and a Honeywell IAQ t-stat if it was my house. I just personally do not like two stage compressors. I would use the largest Kw eletric heat your current eletrical will handle and stage it off into 2 stages. Also ask about upgrading to a 10 year parts and Labor. Spend some money now and becomfortable while saving money later. Just my 2 cents.
A multi zone system might be a viable option.
Cold Feet
07-29-2009, 07:31 PM
Reps have told me w/ a 5-ton unit it is almost impossible to meet the standards for the 30% federal tax credit.:( Apparently Carrier doesn't have one. One rep says Trane has one in the 15-16 SEER range.
Consider two separate 2 ton units and air handlers ducted to serve half your house each. Tax credit compliant 2 ton units are plentiful and two separate systems will give you better temperature control.
Also look at Daikin's 2MXS18GVJU and Sanyo's CMH1972. These are tax credit compliant ductless multisplits. Their main claims to fame are variable capacity (they can't be oversized), considerable heat generation at low temperatures (less need for heat strips), and support for room-by-room zoning.
BobbyBJr
07-29-2009, 08:54 PM
Well, everyone has an opinion and here is mine...lol. First of all, if you truly have 22% duct leakage and your present system did a good job, then it is oversized. The load on my home, which is similiar to what you describe, is barely over 3 tons total, but you need someone to do a load on yours to be sure. I also have two stage equipment in my own home and never knew we could be this comfortable. I rarely notice either of them running in high speed.
vanenk
08-02-2009, 09:45 PM
Sorry about the wait, I've been at work last few days, hardly any time to look at all replies. I appreciate everyone's ideas. What about these:
The Trane rep indicated a two-stage system would run longer while in "low," and be more effective at removing humidity. Is this accurate? I am looking to encapsulate our crawlspace this fall, and I have a feeling this will help to reduce/control humidity better.
Is it money well spent? Some have the opinion that 2-stage systems are more prone to breakdown than single-stage--any basis for this, or just opinion? BDW, could you elaborate on your experience with 2-stagers?
I don't think a zoned system solution is for us. I'm guessing it would require quite a bit of rework (duct, electrical, etc.) and ROI time would far exceed our expected stay. I'll ask, though.
Again, thanks for all the input.
bdw293
08-03-2009, 03:21 PM
I have installed them and just personally do not like them. My main reasoning is alot more electronics in the condensers. With the rheem 2 stage you don't have your typical contactors you have drive boards. Good luck getting one of those quick if it fails. I like keeping things simple units that have standard parts , contactors. If your unit quits chances are the tech will probably have a part handy not so on the 16 seer stuff. Also the price jump between 15 and 16 seer didn't show a good ROI for one seer. We are now a American Standard dealer and I haven't installed any of their 2 stage equipment. I am speaking about my experience with rheem 16 seer 2 stage. Which I would not have ( to many expansion valve problems). I also was skeptical when I was told if a compressor fails in a rheem 2 stage they give you a new condenser not a new compressor. Which tells me they have had problems with field installed replacment compressors. So when the 10 year warranty is up and your comp fails your buying a new unit or taking a gamble with a expensive compressor. It does however provide great cooling comfort and they mostly run on the 1st stage. Just my 2 cents I'm sure their are alot of guys who love them. Just not me. I do like going to a variable speed blower for humidity though.
vanenk
08-04-2009, 10:58 AM
Thanks, bdw. Some good info to consider.
Powered by vBulletin® Version 4.2.0 Copyright © 2013 vBulletin Solutions, Inc. All rights reserved.