gwschubert
07-18-2009, 10:25 PM
Hello Newbe here. I have a 2 ton split system here in Texas I came to check it out because the Condenser triped sometime yesterday.
I found the fan motor died I changed it out and started the unit. The evap and airhandler in in the attic horazonal unit. I hooked the gages and the low side was at 25 deg ( 50 psi) R22 and high side was 120 deg (350 psi) the problem is the evap is cool 45 deg house vent 65 deg. The evap is using an orfice ont a valve.
The liquid line from condenser is hot the Suction line from the condenser is cool not sweating.
Temp is slowly droping but....
Any suggestions. As I have talked to all my mentors here they all !!!!???!!!??? no clue
I found the fan motor died I changed it out and started the unit. The evap and airhandler in in the attic horazonal unit. I hooked the gages and the low side was at 25 deg ( 50 psi) R22 and high side was 120 deg (350 psi) the problem is the evap is cool 45 deg house vent 65 deg. The evap is using an orfice ont a valve.
The liquid line from condenser is hot the Suction line from the condenser is cool not sweating.