jdhall
07-18-2003, 10:51 PM
Here's another reason for not working for a Subway.
This is from a compressor failure/replacement I just
went through. Notice that there are two liquid line
filter driers on this unit, and one is on the
hot-gas/discharge line before the reversing-valve.
No, it's not a muffler! To add to this; the condensing
unit is three floors above the fan coil units( about 130ft run), with no oil return protection; ie. traps or
double suction riser. Only one drier on this unit now,
but the owner doesn't want anything done with the line
set. I told him it will fail again! I'm not paying
for the next compressor, it's in writing!
http://www.wwwebworks.com/talkpics/wallofshame/149887_Die_Again.jpg
[Edited by Boss on 12-29-2003 at 11:51 AM]
This is from a compressor failure/replacement I just
went through. Notice that there are two liquid line
filter driers on this unit, and one is on the
hot-gas/discharge line before the reversing-valve.
No, it's not a muffler! To add to this; the condensing
unit is three floors above the fan coil units( about 130ft run), with no oil return protection; ie. traps or
double suction riser. Only one drier on this unit now,
but the owner doesn't want anything done with the line
set. I told him it will fail again! I'm not paying
for the next compressor, it's in writing!
http://www.wwwebworks.com/talkpics/wallofshame/149887_Die_Again.jpg
[Edited by Boss on 12-29-2003 at 11:51 AM]