toptech
06-22-2009, 12:04 AM
This always happens on saturday after the supply house closes.
Beer Cooler, walk in, 38F design temp
KATA-015E-800-TAC (medium temp r-22)? All data says its R12!!
Been running a year.
New expansion Valve EGVE 1-1\2 sweat
Sporlan distributor with 1\4 stamped on the nozzle(4 tubes) .024 tons?!!
Compressor RLA 5amps Pulling 10-11 amps with clear sight glass
Pulled head, no visible damage. Oil level correct and churning in the sight glass
approx 48\250 psig
Comp superheat 15-22
subcool 8-12
Right on ythe comp tag is 22 stamped
you'd figure this is an r-22 comp?
My question is all data mentions 12,134,404etc, no r-22
Assuming it isnt an r-22, will incorrect refrigerant cause the excessive amps alone?
The pattern is extreme Hunting by the TEV
sight glass full, superheat @ 15 then the glass will empty out, superheat tanks high, subcool will go from 10(full glass) down to 0 flashing.
This sequence will happen every 3 or 4 min
How I have near normal SH with what I believe to be an undersized orifice is beyond me.
Compressor overheats and cycles off every 30 min or so.
Its been awhile for me guys, what are your thoughts.
Compressor is still in warranty
Im looking at replaceing
Compressor(proper type)
New nozzle
new TEV, data says this comp 11,000 and some change with a 20F coil
Tell me Im crazy!
Thanks
Beer Cooler, walk in, 38F design temp
KATA-015E-800-TAC (medium temp r-22)? All data says its R12!!
Been running a year.
New expansion Valve EGVE 1-1\2 sweat
Sporlan distributor with 1\4 stamped on the nozzle(4 tubes) .024 tons?!!
Compressor RLA 5amps Pulling 10-11 amps with clear sight glass
Pulled head, no visible damage. Oil level correct and churning in the sight glass
approx 48\250 psig
Comp superheat 15-22
subcool 8-12
Right on ythe comp tag is 22 stamped
you'd figure this is an r-22 comp?
My question is all data mentions 12,134,404etc, no r-22
Assuming it isnt an r-22, will incorrect refrigerant cause the excessive amps alone?
The pattern is extreme Hunting by the TEV
sight glass full, superheat @ 15 then the glass will empty out, superheat tanks high, subcool will go from 10(full glass) down to 0 flashing.
This sequence will happen every 3 or 4 min
How I have near normal SH with what I believe to be an undersized orifice is beyond me.
Compressor overheats and cycles off every 30 min or so.
Its been awhile for me guys, what are your thoughts.
Compressor is still in warranty
Im looking at replaceing
Compressor(proper type)
New nozzle
new TEV, data says this comp 11,000 and some change with a 20F coil
Tell me Im crazy!
Thanks