PDA

View Full Version : New Condenser and old lineset?



uk4545a
05-13-2009, 01:11 PM
I am replacinf a 22 year old 1.5 ton condensing unit which I venture to guess is a 10 SEER. By moving to a 13 SEER will it be necessary to chnge the lineset's out for larger ones?

Also, is it mandatory to change the coil aboive the fuurnace out if I put this new condensing unit in?

Thanks for any help.

Ken/Atlanta

2old2rock
05-13-2009, 02:00 PM
Lineset - maybe. Indoor coil - yes.
If you're not in the trade, you could be looking at a heap of trouble doing this yourself.

uk4545a
05-13-2009, 02:02 PM
Not doing it myself, just getting different opinions on what is required.

sktn77a
05-13-2009, 04:50 PM
Change the lineset if you can. The additional cost is well worth the insurance/peace of mind against future failure. If it's not practical to change (running under a cement slab/ encased in walls) and it passes the leak test and size requirements, you should be OK (make sure it's thoroughly cleaned out). Being a 1.5 ton unit, the size will probably be fine.

It's generally not a good idea to pair up a nice, new, outdoor condenser with a grungy old mismatched coil!

beenthere
05-13-2009, 06:02 PM
If you want to get your money's worth from a new 13 SEER condenser. Then you'll change out the indoor coil.

sandpipertech
05-13-2009, 07:28 PM
First find out what kind of refrigerant is going to be used. If you are simply replacing the outdoor unit it will use R22. If this is the case don't worry about the lineset. BUT....DON'T just replace the outdoor unit. For a couple of reasons. First you loose all your SEER rating on the new unit if you put it with a old indoor coil. This could also cause damage to the new compressor. Second, R22 equipment is being phased out this year. I would suggest replacing the outdoor unit and coil with R410A refrigerant. Otherwise you will have to replace the coil inside by the end of the year to be sure you can find one that is R22 compatible. If you do go the R410A equipment I would suggest replacing the lineset or at the very least flushing it out because R22 and R410A oils in the lineset will not get along very well :)

beenthere
05-13-2009, 07:40 PM
Second, R22 equipment is being phased out this year. I would suggest replacing the outdoor unit and coil with R410A refrigerant. Otherwise you will have to replace the coil inside by the end of the year to be sure you can find one that is R22 compatible.

Not true.

R410A coils are also rated to work withR22.

So no problem getting parts/coils for R22 systems. Next year, or the next, or the next, etc.

sandpipertech
05-13-2009, 07:45 PM
ABSOLUTELY disagree. This is completely false. How could they be compatible if R410A oil and R22 oil isn't compatible. They sell flush kits for that very reason. I'm not quite sure what you mean by they are rated to work with R22 coils. This isn't true also because the operating pressures of 410a are much highger than 22 and require different TXV valves/fixed orifices...
...also....I do realize that some manufacturers offer coils that are shipped configured with a R22 TXV/orifice that can be changed to R410A. I simply do not believe this is a good way to go based on what I said earlier. I don't see this done very often and the only company around my area that does it is currently on probation with the state:)

beenthere
05-13-2009, 08:08 PM
Because when you buy a new coil.

It doesn't have oil in it. So it doesn't matter weather its going to be used on a R22 or R410A system.

Most manufacturers. Just tested their r22 coils for the higher pressures. And when the coils held, they said they are rated safe for R410A.

R410A coils aren't made any thicker then R22 coils.

jstjohnz
05-13-2009, 08:52 PM
ABSOLUTELY disagree. This is completely false. How could they be compatible if R410A oil and R22 oil isn't compatible. They sell flush kits for that very reason. I'm not quite sure what you mean by they are rated to work with R22 coils. This isn't true also because the operating pressures of 410a are much highger than 22 and require different TXV valves/fixed orifices...
...also....I do realize that some manufacturers offer coils that are shipped configured with a R22 TXV/orifice that can be changed to R410A. I simply do not believe this is a good way to go based on what I said earlier. I don't see this done very often and the only company around my area that does it is currently on probation with the state:)

All of the current Aspen coils seem to be designed for both R410A and R22. One size smaller orifice spec'd for R410A.

If there is a reason that any R410-rated coil wouldn't work with R-22 (with the proper orifice or TXV) I would like to hear the explanation.

beenthere
05-13-2009, 09:33 PM
No reason what so ever.

sandpipertech
05-13-2009, 09:40 PM
Johnz,
Let me try an explain it again. I guess I'm no good at typing what I wanna say. Yes. If you purchase a coil you can convert that coil to work with 22 or 410. The ONLY thing that I am saying is I would not recommend converting it to 410 once its been run using 22. Or vice versa. I've seen too many customers replace their indoor coil with a 22 txv/orifice just to get by. Then replace their outdoor unit in 410a and convert their coils txv or orifice to match. And then their compressor craps out because the coil had 22 oil residue that didn't work with the oils in 410a. I'm simply saying. Choose a refrigerant and stick with it.

fenian
05-14-2009, 07:51 AM
[QUOTE=sandpipertech;3307422]Johnz,
Let me try an explain it again. I guess I'm no good at typing what I wanna say. Yes. If you purchase a coil you can convert that coil to work with 22 or 410. The ONLY thing that I am saying is I would not recommend converting it to 410 once its been run using 22. Or vice versa. I've seen too many customers replace their indoor coil with a 22 txv/orifice just to get by. Then replace their outdoor unit in 410a and convert their coils txv or orifice to match. And then their compressor craps out because the coil had 22 oil residue that didn't work with the oils in 410a. I'm simply saying. Choose a refrigerant and stick with it.[/QUOT

op was asking about lineset and indoor coil.

beenthere
05-14-2009, 07:58 AM
Johnz,

The ONLY thing that I am saying is I would not recommend converting it to 410 once its been run using 22. Or vice versa. I've seen too many customers replace their indoor coil with a 22 txv/orifice just to get by. Then replace their outdoor unit in 410a and convert their coils txv or orifice to match. And then their compressor craps out because the coil had 22 oil residue that didn't work with the oils in 410a. I'm simply saying. Choose a refrigerant and stick with it.


Not anywhere near what you said in your other post.



Second, R22 equipment is being phased out this year. I would suggest replacing the outdoor unit and coil with R410A refrigerant. Otherwise you will have to replace the coil inside by the end of the year to be sure you can find one that is R22 compatible.

You implied he wouldn't be able to get an R22 coil next year.