Bill NC
05-06-2009, 12:58 PM
I just had a new Trane heat pump system installed in my house.
AHU: 4TEE3F40B1000AA
Cond: 4TWX5030A1000AA
The return air system for my old unit may have been undersized, however it seemed to work fine for 17 years.
The estimator told me that I would need 2 - 14x20 floor grates for returns (filter at the AHU). This seemed excessive to me, so I tried reading up on return air systems online (I'm a general contractor).
The new system is a 2.5 ton system (AHU is 3.5 ton to bump up the efficiency). Installed in a non-vented crawlspace.
From what I picked up online, using rules of thumb, I came up with the following:
We need approx. 200 sq in of filter rack area per ton.
2.5 tons x 200 = 500 sq inches of filter (so probably a 20 x 25 filter).
The free area of a filter is about 50% of the actual size, so I need about 250 sq inches of return duct and 250 sq inches of net return grill area.
Two sources of return air (1) oak return air grills at the risers of the stairs and (2) a panned section of floor joists with an existing 14 x 14 grill (no filter) at one end.
(1) The wood grills at the stair risers have a total free area of 40 sq inches.
(2) The panned joist plenum will have a grill at either end, and a drop to the return air box at the AHU almost directly below an existing 14 x 14 grill witl 156 sq in oc free area per the grill manufacturers website.
Their installer installed about a 3-4' section of 14" flex almost directly under the existing 14 x 14 return air grill. The cross sectional area of a 14" circle is 154 sq in. And the flex has a very sharp bend in it that significantly reduces it's area.
So, it would seem logical that right now the 14" flex is the bottleneck, and I may or may not need to add a second grill at the other end of the panned joists.
I've asked the installer to bring a manometer on Monday to help figure out what we need to do.
The tag on the AHU reads: "Tested at 0.5: W C external static pressure".
When he gets here, what would you suggest that we do?
Exactly where would we test for the pressure in the duct system?
What results would indicate that we are getting enough return air flow?
Should we upsize the piece of flex as a first step, retest, then add another floor grill only if we still are not getting enough return air to the AHU?
Thanks in advance for your help with this.
Bill
AHU: 4TEE3F40B1000AA
Cond: 4TWX5030A1000AA
The return air system for my old unit may have been undersized, however it seemed to work fine for 17 years.
The estimator told me that I would need 2 - 14x20 floor grates for returns (filter at the AHU). This seemed excessive to me, so I tried reading up on return air systems online (I'm a general contractor).
The new system is a 2.5 ton system (AHU is 3.5 ton to bump up the efficiency). Installed in a non-vented crawlspace.
From what I picked up online, using rules of thumb, I came up with the following:
We need approx. 200 sq in of filter rack area per ton.
2.5 tons x 200 = 500 sq inches of filter (so probably a 20 x 25 filter).
The free area of a filter is about 50% of the actual size, so I need about 250 sq inches of return duct and 250 sq inches of net return grill area.
Two sources of return air (1) oak return air grills at the risers of the stairs and (2) a panned section of floor joists with an existing 14 x 14 grill (no filter) at one end.
(1) The wood grills at the stair risers have a total free area of 40 sq inches.
(2) The panned joist plenum will have a grill at either end, and a drop to the return air box at the AHU almost directly below an existing 14 x 14 grill witl 156 sq in oc free area per the grill manufacturers website.
Their installer installed about a 3-4' section of 14" flex almost directly under the existing 14 x 14 return air grill. The cross sectional area of a 14" circle is 154 sq in. And the flex has a very sharp bend in it that significantly reduces it's area.
So, it would seem logical that right now the 14" flex is the bottleneck, and I may or may not need to add a second grill at the other end of the panned joists.
I've asked the installer to bring a manometer on Monday to help figure out what we need to do.
The tag on the AHU reads: "Tested at 0.5: W C external static pressure".
When he gets here, what would you suggest that we do?
Exactly where would we test for the pressure in the duct system?
What results would indicate that we are getting enough return air flow?
Should we upsize the piece of flex as a first step, retest, then add another floor grill only if we still are not getting enough return air to the AHU?
Thanks in advance for your help with this.
Bill