While setting up an exception schedule in MSEA Rev. 4 can I also adjust a setpoint as well as the start and stop times? ie. after setting up an exception scedule to run an AHU on a sat which is normally unocc. I want to reset the discharge air setpoint to something other than the normal setting. can this be done?
Nate

NickDeal
03-22-2009, 01:38 AM
I would hit an interlock that would override the setpoint to the new value and when the schedule ends release the interlock and the override.

sssr
03-22-2009, 04:05 AM
Or you could do a control system and bring in the time module and set it so between day 6 (sat) and day 7(sun) the discharge air temp is a different value

nwassers
03-23-2009, 12:45 PM
Not quite sure how to do the whole timer thing.. But I did manage to get the Control Interlock set up. Hopefully this works. I'll see on the 27th of March.
Thanks for your help.

buzzman
03-30-2009, 08:26 PM
nate,
Did it work?

nwassers
03-31-2009, 06:54 AM
I dunno, I jumped the gun and set the temp before I left for day to be sure it set back.