jogas
03-08-2009, 03:06 PM
I was commissioning a College Dorm job yesterday where we put in a JACE with a LON/CGA interface, and an IO-34. When it came to the CGA chiller, I found out that if the chiller sees flow before it receives a start command, it goes into alarm as it wants to control the CHW pumps. Only problem is the CGA can't do Lead/Lag/Failover for 2 pumps. Luckily I had our Electrician run 2 extra cables between the chiller and our Tridium panel. I ended up using an extra cable to bring the CGA's "Solution Pump" contact into the IO-34 as an input to enable our CHW pump logic.
I don't understand Trane's thinking, as the Solution Pump contact can be set to Run (always closed), or Auto (cycles as chiller requires). We obviously set it to Auto and the chiller startup/shutdown sequence worked fine.
Thoughts....anyone?