homeowner12345
12-18-2008, 07:23 AM
I have a suspicion that the Outdoor Reset sensor/programming on my recently installed Peerless Pinnacle is not working correctly (or at all). How can I tell for certain?
The device appears to be wired correctly, and the Pinnacle manual says that, "When this sensor is installed the control will automatically recognize it and begin outdoor reset operation."
However, as an example, the outdoor temperature (according to the Weather Channel) is currently 21 deg F in my area; accessing the Pinnacle's control module, the sensor indicates 32 deg F. Okay, I'll consider that a possibility (brick house retains heat, sensor on North side) ...
According to the manual, "When the outdoor temperature is above the outdoor design temperature and below the mild weather outdoor reference temperature, the boiler target temperature will vary according to a straight line between the design point and the mild weather reference point. For example, if the outdoor temperature is at 32ºF the boiler target temperature
will be 144ºF."
The Outdoor Design Temperature is set at 5 deg F, Mild Weather Outdoor Reference Temp is at 68 deg F.
Even so, when the boiler recently came on to satisfy Zone 2 demand for heat, the boiler rapidly ramped up to 180 deg F (factory default Boiler Supply Design Temperature *and* Supply Set Point Temperature). Should it not have maxed out at 144? Or, am I totally misunderstanding the principles involved here?
The device appears to be wired correctly, and the Pinnacle manual says that, "When this sensor is installed the control will automatically recognize it and begin outdoor reset operation."
However, as an example, the outdoor temperature (according to the Weather Channel) is currently 21 deg F in my area; accessing the Pinnacle's control module, the sensor indicates 32 deg F. Okay, I'll consider that a possibility (brick house retains heat, sensor on North side) ...
According to the manual, "When the outdoor temperature is above the outdoor design temperature and below the mild weather outdoor reference temperature, the boiler target temperature will vary according to a straight line between the design point and the mild weather reference point. For example, if the outdoor temperature is at 32ºF the boiler target temperature
will be 144ºF."
The Outdoor Design Temperature is set at 5 deg F, Mild Weather Outdoor Reference Temp is at 68 deg F.
Even so, when the boiler recently came on to satisfy Zone 2 demand for heat, the boiler rapidly ramped up to 180 deg F (factory default Boiler Supply Design Temperature *and* Supply Set Point Temperature). Should it not have maxed out at 144? Or, am I totally misunderstanding the principles involved here?