Our school system has 30 buildings and we control with Metasys PMI. A couple of the schools have room zone temperatures named with the room number followed by ZT. 1ZT, 2ZT, etc.

The other buildings just use ZT for the zone temp and it is easy to do a summary.

I would like to know if there is a wild card that I can substitute for the number so that I can do a summary of the room zone temperatures.

NINAX
10-10-2008, 05:56 PM
Here's the capabilities.

OWS User's Manual (http://cgproducts.johnsoncontrols.com//MET_PDF/120165.PDF)

Chapter 38

richlaf
10-10-2008, 07:18 PM
That worked. I had to do a summery for the single digit room numbers and another summery for the double digit room numbers. It's still a whole lot easier than looking at the rooms one at a time.