08-01-2008, 11:58 AM
Ok, Unit Was Installed 3 Months Ago, I Get The Call, Unit Is Off On Low Pressure Lock Out.
Readings
73deg R/a
57deg S/a
80 Deg Amb
Suct 58 Psi 32 Sat
Dis 235psi 112 Sat
S/h 43 Deg
Sub 28 Deg
Comp Amps 18.7
Name Plate Amps 18.9 Rla
Filters Removed Coil Is Clean Cond And Evap
Indoor Fan On High
I Was Told A Tech Had Been There Before But They Werent Sure What He Did.
Im Going Today To Remove The Ref And Change Drier,blow Out With Nit And Start Fresh
Im Trying To Bring My Postings Up So You Can Reply With Some Suggestions
Thanks
James