r404a
07-31-2008, 12:53 AM
MOD# YS DA CA S2-CJA SER# SAYM 912448
I punched tubes on the cond earlier this year due to high cond approach, current limit issues and oil filter warnings. Also changed the filter at that time. The filter I pulled was a 3 micron and I went back with a 12 micron, which york had listed as the right part. If anything, that would have alleviated premature clogging.
Machine ran for about a month and a half and then I got the call that facilities had to reset twice on clogged filter diagnostic. I ordered a new filter before going out and decided to start there. Went with another 12 micron filter and brought back online. Saw the warning a few times. Piped in brass "t" fittings at both transducers to get real time readings against 1 analog gauge- the pressures and pressure differential were identical to the ones read at the micro.
Basic running conditions: 44 leaving evap @ 65 psig suction/ 178 condenser pressure at 85 entering water@ 66 %RLA with 20 psid on the oil line. There is an oil solenoid and an oil cooler inbetween the transducers and I have no pressure tap between the two, but I am seeing almost no pressure drop across the filter itself.
I noted that the oil solenoid coil was getting very hot, 190 degress, and I changed it for good measures, to no avail. I don't see that 20 psid is so high, but york does. Any ideas?
I punched tubes on the cond earlier this year due to high cond approach, current limit issues and oil filter warnings. Also changed the filter at that time. The filter I pulled was a 3 micron and I went back with a 12 micron, which york had listed as the right part. If anything, that would have alleviated premature clogging.
Machine ran for about a month and a half and then I got the call that facilities had to reset twice on clogged filter diagnostic. I ordered a new filter before going out and decided to start there. Went with another 12 micron filter and brought back online. Saw the warning a few times. Piped in brass "t" fittings at both transducers to get real time readings against 1 analog gauge- the pressures and pressure differential were identical to the ones read at the micro.
Basic running conditions: 44 leaving evap @ 65 psig suction/ 178 condenser pressure at 85 entering water@ 66 %RLA with 20 psid on the oil line. There is an oil solenoid and an oil cooler inbetween the transducers and I have no pressure tap between the two, but I am seeing almost no pressure drop across the filter itself.
I noted that the oil solenoid coil was getting very hot, 190 degress, and I changed it for good measures, to no avail. I don't see that 20 psid is so high, but york does. Any ideas?