chiller rob
07-28-2008, 10:59 PM
Gents,
I have a customer that was having some star delta starter problems and subsequently went with a benshaw soft starter... we had to get creative with current feedback to the CCM-U1, to get the proper current feed back for FLA. -8.25VDC @ 100. no biggie... units been running great...
3 years later he is having some problems with the control panel.. unit not loading on startup until the vane operator is placed in manual load and then back to auto and it will work. checked chilled water sensor ok, and first stage of freeze stat is ok...
He was sold a upgrade for the CCM U1, turns out it is a MOD 182... this is a physically larger controller and you have to drill a 3rd 1/4 hole for mouniting and the knobs are smaller... also part of the kit is a new chilled water sensor...
The installation instructions are the same as Mod 12... and yes i have upteenth times checked my dip switches...
problem...
1. the new controller is not seeing my -8.25 VDC feed
back from the starter at V1,V2 in the new panel... worked fine in the old one...
2. the new controller by what i am reading is looking for -0-10 VDC @ 100 FLA...
3. I tested the circuit with a 9 volt battery with the demand limit set at 70% machine unloaded with new control.
4. the benshaw A/O is weak and the scale is wide at 0-10 vdc for 0 - 200% amps...
Factory said that they were having problems with this panel recieving the signal from the black box (which i no longer have) and had a converter component that rescaled the signal and amplified it so the new CCM would see it...
I have looked in all my files and I dont have anything on this...
The only thing I could find was the CH 531 starter retrofit kit...
Has anyone seen this before? This is in a critical health care facility any help apprecieted...
Thanks...
I have a customer that was having some star delta starter problems and subsequently went with a benshaw soft starter... we had to get creative with current feedback to the CCM-U1, to get the proper current feed back for FLA. -8.25VDC @ 100. no biggie... units been running great...
3 years later he is having some problems with the control panel.. unit not loading on startup until the vane operator is placed in manual load and then back to auto and it will work. checked chilled water sensor ok, and first stage of freeze stat is ok...
He was sold a upgrade for the CCM U1, turns out it is a MOD 182... this is a physically larger controller and you have to drill a 3rd 1/4 hole for mouniting and the knobs are smaller... also part of the kit is a new chilled water sensor...
The installation instructions are the same as Mod 12... and yes i have upteenth times checked my dip switches...
problem...
1. the new controller is not seeing my -8.25 VDC feed
back from the starter at V1,V2 in the new panel... worked fine in the old one...
2. the new controller by what i am reading is looking for -0-10 VDC @ 100 FLA...
3. I tested the circuit with a 9 volt battery with the demand limit set at 70% machine unloaded with new control.
4. the benshaw A/O is weak and the scale is wide at 0-10 vdc for 0 - 200% amps...
Factory said that they were having problems with this panel recieving the signal from the black box (which i no longer have) and had a converter component that rescaled the signal and amplified it so the new CCM would see it...
I have looked in all my files and I dont have anything on this...
The only thing I could find was the CH 531 starter retrofit kit...
Has anyone seen this before? This is in a critical health care facility any help apprecieted...
Thanks...