07-24-2008, 07:28 PM
stopped in on 1 of mine - (2) yt design 'j' electro-mechanical starters.both run remote by bas. machine online purring like a kitten.
the other machine off - ready to start - in the box where fault is listed - motor pulldown limit. THE MACHINE WAS OFF!!. won't reset on the panel toggle, had to de-energize & reboot to reset. didn't show in the history section,(but why would it). i have a tinge saying this will reappear again, probably limiting the machine on a day when the sh@t hits the fan with the dog days rapidly approaching
any comments? :confused:
heavymetaldad
07-27-2008, 08:42 PM
what - no ones seen this? hey, york guys - anything???
yorkdude
07-27-2008, 11:40 PM
hmmmm..............
york56
07-28-2008, 06:05 AM
What happens when you switch or run machine in local mode in optiview panel
stickerhead
07-28-2008, 01:41 PM
Was the panel in "remote" or "ISN"?
heavymetaldad
07-28-2008, 08:47 PM
machine room is run remotely. when the message was seen - machine was off line, ready to start. thanks for response
stickerhead
07-30-2008, 10:53 AM
Let me re-phrase. Are they talking to a microgateway or just a contact closure?
heavymetaldad
07-30-2008, 08:09 PM
Let me re-phrase. Are they talking to a microgateway or just a contact closure?
i'm sure it's not relay logic. they change setpoint from their room downstairs, they've had previous issues with the siemens automation. (phantom chiller starts w/ no a/h's in the wee hours.had multiple hi disch. temp. failures. siemens techie found the start command buried deep in his program.)
if bas would limit loading, would it be displayed w/ machine off? (ready to start?) why, then , did the message 'reset' (disappear) when rebooting? (the opti) but,you got me thinking, that this may be an issue with the automation.
thanks for your reply
stickerhead
07-31-2008, 09:19 AM
I should be easy to tell. If there is a 3x4 board mounted in the top left side of the Optiview, it has a microgateway. Whether they are using it or not,you would have to check. Sounds like they are. Could be a communication problem between them.
stickerhead
07-31-2008, 09:19 AM
If it is new, they could be using the "e-link"
heavymetaldad
07-31-2008, 07:21 PM
believe it's a gateway. bldg. had field installed 2-3 yrs. ago, to tie in automation.