View Full Version : Carrier leaky coils
superd77
07-16-2008, 11:12 PM
I got this long time customer with a Carrier air handler.(Trane outside)
Since 2002 I've put in 3 evaporator coils. Now its leaking again.:eek:
I sold the customer a new system.(Lennox)
All exposed copper in the attic is black. :confused:
Have any of you pros seen this before???? What might be the risk to the new unit??? OR, is this just a Carrier thing????.......I have seen this alot out of Carrier but not this bad..
Thanks!!:):D
adrianf
07-16-2008, 11:15 PM
Well water?
superd77
07-16-2008, 11:27 PM
Pretty sure he is, not 100% though.
House is on the lake. No swimming pool.
adrianf
07-16-2008, 11:47 PM
If the house doesn't smell like sewer gas. I'd be looking at sulfar gas from the ground water. We have areas of the county that have higher than normal coil failures and it's from the sulfar in the ground water. sprinklers just have to atomize the gas not even wet the coil. It can go up soffits, and it they use it in the house it will be everywhere.
ISOTHERMAL
07-17-2008, 12:37 AM
I checked a york unit the other day, the suction line where it entered the evap coil was missing the arma flex inso for a short distance was black, in another spot the arma flex was missing and the copper was black there also. The unit was low on refrigerant, the evap coil was in bad shape, all return bends, feeder tubes and suction header was black. (evap had multiple leaks). The liquid line and all exposed copper outside looked like you would expect 10yr old copper to look. They have sulpher water, I have heard others mention it as well that the sulpher is the culprit. The evap coil had been replaced also. Another thing they mentioned was that there washing machine tub rotted out rather quickly.
adrianf
07-17-2008, 01:18 PM
I checked a york unit the other day, the suction line where it entered the evap coil was missing the arma flex inso for a short distance was black, in another spot the arma flex was missing and the copper was black there also. The unit was low on refrigerant, the evap coil was in bad shape, all return bends, feeder tubes and suction header was black. (evap had multiple leaks). The liquid line and all exposed copper outside looked like you would expect 10yr old copper to look. They have sulpher water, I have heard others mention it as well that the sulpher is the culprit. The evap coil had been replaced also. Another thing they mentioned was that there washing machine tub rotted out rather quickly.
they need a water treatment company.
ISOTHERMAL
07-17-2008, 03:23 PM
they need a water treatment company.
I agree.
superd77
07-17-2008, 10:22 PM
Thanks for the info. I couldn't get in touch with the customer today. Will post back tomorrow.
superd77
07-22-2008, 10:46 PM
I talked with the customer today. Hes on city water. No well!:(
This guy is a fishing guide. He makes his own lures. Out of lead.
He heats the lead and casts fishing spoons. Could this have anything to do
with his leaky coils? :confused: I'm starting to think this is just a Carrier
thing.:D
adrianf
07-23-2008, 01:22 PM
A gentleman called me after being refferd to. His story went like this.
He has had multiple indoor coil failures in his home. He has two systems which he replaced one of the indoor units to a differnt brand after repeated failures. The installing company has done all the service they will do until he determines what is killing the coils. Different manufacturers with multiple failures in the same house. His silverware tarnishes rapidly also. The gentleman is even taking and placing silverware in neighbors homes that haven't had the a/c problems he's had and the silverware does not tarnish.
If it's a manufacturer coil problem they just look like a/c coils, if it's corrision of some kind the coppr will be all black maybe even with some tourtise like reflections in the sun light. Reduced air flow for long periods of time will show as excessivive rusting on the galvanized end plates. HTH
No sewer gas smell correct? Sprinkler sytem?
superd77
07-23-2008, 07:03 PM
A gentleman called me after being refferd to. His story went like this.
He has had multiple indoor coil failures in his home. He has two systems which he replaced one of the indoor units to a differnt brand after repeated failures. The installing company has done all the service they will do until he determines what is killing the coils. Different manufacturers with multiple failures in the same house. His silverware tarnishes rapidly also. The gentleman is even taking and placing silverware in neighbors homes that haven't had the a/c problems he's had and the silverware does not tarnish.
If it's a manufacturer coil problem they just look like a/c coils, if it's corrision of some kind the coppr will be all black maybe even with some tourtise like reflections in the sun light. Reduced air flow for long periods of time will show as excessivive rusting on the galvanized end plates. HTH
No sewer gas smell correct? Sprinkler sytem?
No sewer smell, and no sprinkler system.
Customer said he had a 25 yr old Carrier system before we put in the one he has now. The drain pan rusted through is the reason he changed it out.
Maybe the older a/h had thicker copper. Newer coils are thinner.
I know something is causing the leaky coils. All exposed copper is black in the attic, None is black outside.
I would like to give him an answer or at least point him in the right direction.
We install the new system next week. Going from R-22 to R-410a.
I hope the new coil doesn't get ate up!!!!:eek:
adrianf
07-23-2008, 08:15 PM
can you get the tinned coil?
superd77
07-23-2008, 09:20 PM
can you get the tinned coil?
Never heard of it. Not sure its an option on Lennox.:confused:
caliweath33
07-23-2008, 10:31 PM
Carrier has the tin coated coils.
lost_art
07-23-2008, 11:23 PM
three words that will haunt you till you've replaced so many warranty coils that your ready to cry, volitle organic compounds (v.o.c.'s). what they need is a media filter with a uv light and thats about all you can do. you've changed brands and your still having leaks its not the equiptment its the enviornment its in.
and of course this didnt become a problem till the new units were put in. you did almost hit the nail on the head with thinner copper but the problem is now the mfgs have hit the balance point of efficency vs. relieability.
according to bryant/carrier this is the cause for most i/d coil leaks but they also state that cloride compounds are the most harmful, but if i recall correctly back in the day every aerosol propellent was a cfc so why is it happening now??? too thin copper for the high eff. ratings. carrier has come out with the tin plated coils and york has their own way of combatting v.o.c.'s.
a uv light w/media filter is your best option till lennox comes out with a way to protect their coils.
the thing to remember is this will only be true in some residence not all. the ones this will work the best is premature coil failures, ie 2-7 yr. range. i dont know why but there are certain condtions that make this worse than others.
i work for a bryant f.a.d. service co. and believe me im tired of doing warranty i/d coils but all we can do is inform the consumer and let them make their decision.
Powered by vBulletin® Version 4.2.0 Copyright © 2013 vBulletin Solutions, Inc. All rights reserved.