View Full Version : Carrier furnace with new A/c and low airflow



Hasty
07-15-2008, 07:37 PM
Hi, I just had A/C installed to my home which is 2 years old. My furnace is a Carrier 58STX90-16 which had great air flow on heat mode throughout my house. I had a local contractor install a Ducane system with a matched 4 ton coil in the attic. He had to move the ducting distribution box to make room for the coil. Since then my air flow has been dismal. I contacted the installer with my problem and he was of little help. I went ahead and contacted another local contractor who came out and said that the unit was 1lb low on freon and he fixed a condensation leak in the attic. He also didn't have an answer to why the low air flow. Now today I've been testing the a/c to see if it could keep my house at 75 degrees. Right now it's 86 outside and the a/c is running constantly and it's 77 inside my home. I checked the small copper line going to the condensor because i was told it should be warm and it's not. Please help with some guidance if you could I'm getting tired of throwing money at this unit with no support from these contractors...

Thank You...

Mike

cnpro18
07-15-2008, 07:43 PM
It sounds like the installing contractor needs to address and fix the problem. Have them do a static pressure test, and check airflow compared to size of unit. A reputable contractor will fix the problem.

beenthere
07-15-2008, 07:44 PM
Well. You may have gone with the wrong bid.
Not to bust on Ducane. But many times its used by lower priced contractors that don't test systems to see if the existing duct work can handle the coils restriction.

Good chance, that as you expect, teh install is not corect.

Can you post pics of teh A/C coil box, and how teh ducts are attached to it.

From your description, we can't tell anything.

Hasty
07-15-2008, 08:03 PM
Thanks for the replies. The original contractor is giving me the run around and as you suspect my budget is tight and I went with the low bid but now my budget is out the window. I'll get some pics posted...

thandar56
07-15-2008, 08:15 PM
whats ur temperature difference between supply and return duct

Hasty
07-15-2008, 11:07 PM
Here are some pics and I'll work on getting the temps.

http://members.cox.net/atayde/P7150052.JPG

http://members.cox.net/atayde/P7150053.JPG

http://members.cox.net/atayde/P7150054.JPG

http://members.cox.net/atayde/P7150055.JPG

Thanks

RyanHughes
07-15-2008, 11:12 PM
Is that a flexible dryer vent on the flue line? Not sure if that's code, but I'd want rigid material to carry those harmful flue gases. If you can get close enough to the distribution box, do you feel any major air loss?

Hasty
07-15-2008, 11:24 PM
The flue is a flexible metal tubing of some sort, I would assume it's code the house was new construction as of 2 years ago but you never know. I checked all around the coil for any significant air loss and I don't feel any. Could it be possible that my blower just isn't strong enough for this coil even though it is supposedly matched or could there be an obstruction between the furnace and coil?

beenthere
07-16-2008, 01:45 AM
That looks like a flexable B vent connector section. Its code approved. Atleast here it is.

It looks like the coil is 3 or 4" narrower then the furnace, and if it is. That means it could be restricting the air flow.

I have no idea why that drain pipe is going in to the supply plenum.

21degrees
07-16-2008, 01:57 AM
That furnace is 1600 CFM Max The plenium Coil looks small better be at least 18" round supply duct or 14" x 20" rect duct coming off plenium. You can increase motor to 2000 CFMs if duct work is not problem

t527ed
07-16-2008, 09:24 AM
that was a take the money and run job......:eek:


since you will probably never see them again you might want to call another contractor to see if it can be straightend out.

Hasty
07-16-2008, 05:42 PM
Yeah it definitely looks and feels like a take the money and run job. At this point I'm trying to locate a competent contractor in my area who can adequately fix my issue. Should I be requesting an increase in the CFM from my blower or is the coil the issue since it is smaller than the furnace? My hopes are that the next contractor will be able to diagnose and fix this properly.

Thanks for the input!

Daltex
07-16-2008, 06:04 PM
Ouch!

The next contractor should check the static before increasing CFM. It could be the coil or the plenum. Glad to see the plenum drain though!:eek:

eetechster
07-16-2008, 06:34 PM
I have seen your pics and im not impressed at all and I am sory that, that happened to you; but not to bust on ducane, but where im from its the equipment of chioce for side work on the fly, I onley hope you whent with a repital co in your area and they will make good on it, if you didn't that's ok but remember you get what you pay for, but im sure you know by now from reading your ansewr lies in a new contractor with good reff's they will be able to help you with your problum, best of luck to you,