jeff520
07-15-2008, 11:14 AM
I have a question about the design of the Trane XL19i and this is the only resource I am familiar with that could possibly provide some insight as to why Trane decided to design it the way that they did.
My unit is a 3 ton, so it has a 1.5 ton compressor for the first stage and a three ton compressor for the second stage. When the thermostat calls for second stage cooling the condensing unit shuts down the little compressor, waits for a while and then starts up the big compressor.
In the conditioned space this is seen as an increase in airflow at the moment the thermostat makes the call for second stage - an increase in temperature of the conditioned air (because no compressors are running and the evap coil can no longer cool) - and then the temperature of the conditioned air falls to the usual 15 to 20 degree drop from ambient as the big compressor starts up.
I understand the reason for the delay is because it is difficult for the compressor to start against the pressure differences present because the earlier running of a compressor left a high pressure on the condenser side and a lower pressure on the evap side, but the Trane TXV is a non bleed type, so a short delay is not going to balance the pressures enough to make for an easier start.
So, finally, here comes the question:
Since the compressors in an XL19i may have to start against the most difficult set of working pressures possible why not accept the fact and make the following design changes
1/ Replace the 3 ton compressor (in the 3 ton unit) with a 2 ton compressor, change the 1.5 to to 1.0 ton.
2/ Change the logic on the control board to run the unit in three stages. One ton, two ton or three ton depending on which compressors were running.
3/ Allow a compressor to start even if one was already running since there is no benefit to waiting for pressures to equalize if the TXV is no bleed.
An alternative might be to make both compressors the same (1.5 tons for this example) and bring the second one on line (together with the first) for high cooling. The control board could also alternate between the two compressors when only first stage was required so that they each had similar run times over the total life of the unit.
Comments?
My unit is a 3 ton, so it has a 1.5 ton compressor for the first stage and a three ton compressor for the second stage. When the thermostat calls for second stage cooling the condensing unit shuts down the little compressor, waits for a while and then starts up the big compressor.
In the conditioned space this is seen as an increase in airflow at the moment the thermostat makes the call for second stage - an increase in temperature of the conditioned air (because no compressors are running and the evap coil can no longer cool) - and then the temperature of the conditioned air falls to the usual 15 to 20 degree drop from ambient as the big compressor starts up.
I understand the reason for the delay is because it is difficult for the compressor to start against the pressure differences present because the earlier running of a compressor left a high pressure on the condenser side and a lower pressure on the evap side, but the Trane TXV is a non bleed type, so a short delay is not going to balance the pressures enough to make for an easier start.
So, finally, here comes the question:
Since the compressors in an XL19i may have to start against the most difficult set of working pressures possible why not accept the fact and make the following design changes
1/ Replace the 3 ton compressor (in the 3 ton unit) with a 2 ton compressor, change the 1.5 to to 1.0 ton.
2/ Change the logic on the control board to run the unit in three stages. One ton, two ton or three ton depending on which compressors were running.
3/ Allow a compressor to start even if one was already running since there is no benefit to waiting for pressures to equalize if the TXV is no bleed.
An alternative might be to make both compressors the same (1.5 tons for this example) and bring the second one on line (together with the first) for high cooling. The control board could also alternate between the two compressors when only first stage was required so that they each had similar run times over the total life of the unit.
Comments?