07-12-2008, 11:50 PM
I am taking a contractors test and I have to do a Manual J 7th edition. I am getting quicker but I need some help this weekend. When I get to the equipment summery, how do I get the Cooling CFM and Heating CFM? I cannot find a description in the Manual J book. I am not a service guy, I am a tinner. After this test I will probably never have anything to do with residential again so don’t think I do not deserve the license for this one question. I can get the answer Monday but thought one of you fellas could help me out before then. I would like to complete two more Manual Js this weekend at home and start on a fresh one Monday. Is there a table in Manual J or is this something from the code book or this just something I should now from experience? Thanks for your time.
Gunslinger
07-13-2008, 12:27 PM
find your SHR by taking the sensible BTUH and adding the latent BTUH. This is the total BTUH. Now divide the sensible by the total. This will give you SHR. If above .85, use TD of 17. If SHR is .8 to . 85, use 19. If below .8 use 21.
Then take sensible divided by 1.1 times Td answer is CFM
AccurateHT
07-13-2008, 12:34 PM
Im a novice in terms of system design,but this seems like a manual S issue.
I looked@ man.J 8th v2 and found in sec.11-21 "procedure for evaluating zoning requirements". Preliminary estimates for block cfm
Aprox.Heating cfm=heating load/(1.1 x ACF x (supply air temp - room air temp))
Aprox.Cooling cfm=sensible load/(1.1 x ACF x (room air temp - supply air temp))
It says 30* is typical heating TD, 20* for cooling
it also states these approximations are ok for zoning decisions but use man.D for dist. system
gypsieking
07-13-2008, 02:11 PM
find your SHR by taking the sensible BTUH and adding the latent BTUH. This is the total BTUH. Now divide the sensible by the total. This will give you SHR. If above .85, use TD of 17. If SHR is .8 to . 85, use 19. If below .8 use 21.
Then take sensible divided by 1.1 times Td answer is CFM
Thanks. You are really helping me out. Let me run this past you.
I have a Sensible gain of 17671 Btu (Calculation Procedure D)
I have a Latent gain of 6044 Btu (Calculation Procedure D)
Add these together I get 23715 Total
Divide 17671 by 23715 = SHR .74514 so I use 21.
21 divided by 1.1 = 19.09091.
19.09091 X 75 TD = 1431.818
So my answer is 1432 CFM Cooling?
If I did this right I really appreciate your help. Now how do I get the heating CFM?
gypsieking
07-13-2008, 02:48 PM
Delta T:
I am not allowed to use anything past 7th edition for this exam manly, I am told, because 7th edition was still long form. To tell the truth I do not even own anything past 7th edition. I am going to look at manual “D” since you brought it up but I am only allowed to take the Manual “J” into the exam. Thanks for the help.
Post Script: Actually the more I look at it, Your qouted formula may be just what I need. Let me put this to pencil some more.
Gunslinger
07-13-2008, 03:01 PM
17671 plus 6044 =23715
17671/23715 = .75 which is SHR
use delta T 21* 1.1 X .75 = 23.1
cfm= 17671/23.1 = 765 cfm
use heat rise for heating
gypsieking
07-13-2008, 03:05 PM
17671 plus 6044 =23715
17671/23715 = .75 which is SHR
use delta T 21* 1.1 X .75 = 23.1
cfm= 17671/23.1 = 765 cfm
use heat rise for heating
Thanks fellas: I may have a chance at this yet.
beenthere
07-13-2008, 03:07 PM
Thanks. You are really helping me out. Let me run this past you.
I have a Sensible gain of 17671 Btu (Calculation Procedure D)
I have a Latent gain of 6044 Btu (Calculation Procedure D)
Add these together I get 23715 Total
Divide 17671 by 23715 = SHR .74514 so I use 21.
21 divided by 1.1 = 19.09091.
19.09091 X 75 TD = 1431.818
So my answer is 1432 CFM Cooling?
If I did this right I really appreciate your help. Now how do I get the heating CFM?
Something wrong with that formula.
Your not going to get a 21°F delta moving 1432CFM with a 2 ton unit. Which is what your sensible load is indicating you need.
gypsieking
07-13-2008, 03:24 PM
Okay. I have just slipped into the darkness again. Let me tell you what I have. I have a winter design temperature difference of 75. A summer design temperature difference of 20. Room Relative Humidity of 55% Daily range of 24m. Design heating load requirement of 70604.5. Cooling is 17671 sensible and 6044 latent. Total cooling load of 23715. Design temp swing of 3 degrees. Ventilation CFM = 100. Can someone walk me through the cooling CFM and Heating CFM of the equipment summery? I guess I really need it spelled out. Gunslingers last formula really spelled it out but I can not get the third line to = the same. Where am I getting off the path?
Gunslinger
07-13-2008, 03:44 PM
3rd line.
use a delta of 21*
1.1 times 21 equals 23.1
sesible of 17671 divided by 23.1 equals 765 cfm
gypsieking
07-13-2008, 08:43 PM
Thanks for everyone's help. I am feeling more confident. I take the exam Wed and should know the result by Friday. I will let you know how I did.
energy_rater_La
07-13-2008, 10:11 PM
Good luck with your exam!
gypsieking
07-19-2008, 11:16 AM
The exam was tough. I believe all my figures where acurate. I got a little rushed the last hour and it looks like a child drew in all the systems on the print but the info was there and done correctly. The exam board had a golf outing Friday so I will get my results Monday afternoon. The exam was eight hours and was worse then my wedding. I will keep you posted.
gypsieking
07-27-2008, 12:07 PM
I passed the manual J. Thanks for all your help.