07-12-2008, 09:08 PM
What is the difference in temp from supply and return air in 410 A. Like the R22 is typically 20 degrees sifference. What is the difference in 410A? What should they do? I have put a 410A in a restauraunt and it is not cooling.
I_bend_metal
07-12-2008, 09:16 PM
Depends on what your other temps are really...what's the question again?
2old2rock
07-12-2008, 09:26 PM
There is no expected difference in temperature differential between the two. We shoot for 20 degrees with either one.
chlosum
07-12-2008, 09:51 PM
did you change evap?
did you change refrig lines or flush?
R-410 is just like any other refrigerant. Understanding your PTR and the refrigeration cycle is key.
dholladay
07-13-2008, 02:49 AM
THIS IS WHATS HAPPENING I HAVE INSTALLED 3- 5TON 410A HEIL PACKAGE UNITS .IN A 2500SQ FT OLD BRICK BULDING THAT HAS COMPLETLY REMOLDED,AND HAS BEEN MADE INTO A RESTARANT/BAR.HOWEVER THE BULDING HAS NO CELING JUST EXPOSED RAFTERS AND DUCT . . WELL WITHOUT WRITING AN ENTIRE BOOK ITS YOUR TYPICAL OLD DOWTOWN BULIDING.ITS HAS BEEN WORKING FINE FOR THE LAST THREE MONTHS. UNTILL THIS PAST TUESDAY SO I CHECKED ALL THE UNITS THEY WERE ALL RUNING .FINE BUT ALL T-STATS WERE SET AT 7O BUT AVERAGE TEMPERATURE WAS 77.SO I DISCOVED THAT THE 410A HEIL UNITS HAVE 1 COMPRESSOR BUT 2 STAGES OF COOLING SO I JUST TIED Y2 AT THE PACKAGE UNIT TO Y1 AND REMOVED FILTERS THAT HADE BEEN LEFT INSIDE INSIDE UNIT FROM FACTORY.THEY LOOKED SOMEWHAT DIRTY AND THERE WERE ALL READY FILTERS INSIDE BULDING SO DIDNT THINK WE NEEDED DOUBLE FILTERS.THE OWENERS SAID THE UNIT WORKED GREAT AFTER THOSE2 CHANGES 4- 3 DAYS ANYWAY. NOW HOWEVER THERE NOT KEEEPING UP IT WAS 78 AT 6.00PM IM WONDERING WHAT THE HELLS SUDDENLY CHANGED. TO CAUSE THE WHOLE BULDING TO STOP COOLING I ONLY PUT THE 410A UNITS IN BECAUSE THEY WERE ALL OUT R22S THE DAY WE HAD TO PUT UNITS ON ROOF.IM STUMPED OR STUPID .I GUESS ITS THE LATER IM LOOKING FOR ANY ANSWERS .ALL DUCT WORK WAS INSTALLED TO ENGINNERS PLANS IM LOST WITH THE 410A :confused:
Tiger93rsl
07-13-2008, 04:41 AM
Check your super heat, ambient temp.,Room temp., Pressures, sub cooling, humidity and temperature drops across the evaporator. One must know all this information before a diagnosis can be made
catmanacman
07-13-2008, 06:28 AM
is the make up air working for the venthood
aintitfun
07-13-2008, 08:31 AM
Hard to say with the info given. But one thing I can tell you for sure, is the R410A is not the cause.
obxtech
07-13-2008, 08:49 AM
What the heat load call for? was all equipment, lighting, ventilation and people included for peak hours? if so most likely the hood's makeup air or lack of would be the most common problem with restaurants.
beenthere
07-13-2008, 12:44 PM
What was the temp on the roof when these units would cool.
Did you check to see if these units meet the engineers sensible cooling specs.
wogpa67
07-13-2008, 01:22 PM
as said it is nothing to do with the units. do you have economizers on any of them? check your damper minimum position and check that make up air fan is working properly
Poodle Head Mikey
07-13-2008, 01:45 PM
.
dholladay
07-13-2008, 11:18 PM
The make up air fan is working properly. The system was installed by engineers specs. I believe there is a maximum of 60 people in the place.
sammy37
07-13-2008, 11:26 PM
The make up air fan is working properly. The system was installed by engineers specs. I believe there is a maximum of 60 people in the place.
Just found your problem, system was installed by engineers specs!:D
superd77
07-13-2008, 11:30 PM
.THE OWENERS SAID THE UNIT WORKED GREAT AFTER THOSE2 CHANGES 4- 3 DAYS ANYWAY. NOW HOWEVER THERE NOT KEEEPING UP IT WAS 78 AT 6.00PM IM WONDERING WHAT THE HELLS SUDDENLY CHANGED. TO CAUSE THE WHOLE BULDING TO STOP COOLING :
Sounds like something else broke. You did say they were Heil, right??:D:D
beenthere
07-14-2008, 12:14 AM
What was the sensible and latent capacities the engineer speced.
How much fresh air is being brought in.
Between the people and hot food, you have around 6.5 tons load.
About another 2 to 3 tons in fresh air.
Then you got lighting load yet. Plus the structures heat gain.
15 tons is cutting it close.
Might be that 15 tons can't handle the peak loads.
TEK723
07-14-2008, 06:46 PM
is the make up air working for the venthood
Good call cat man!
diverdan
07-14-2008, 08:40 PM
Quit screaming and get rid of typing in all caps. It's not only rude it's very hard to read.