How can i convert a 12 vdc power supply to produce 4-20 ma?
Need something simple to test actuators and vfd signal inputs.
I don't really want to spend the money on a fluke process meter because i don't do controls all the time.

absrbrtek
06-29-2008, 06:16 PM
Buy a Kele signal generator. Think mine was about $150 a few yrs ago.

jcrank
06-29-2008, 06:52 PM
I also have one of the Kele signal generators. It works very well.

Here is a link with more information on it
http://www.kele.com/olcat/TE7/ASG.PDF

twisted pair
06-29-2008, 07:28 PM
I have used one from ACT. It is in the same price range as the one from Kele.

http://www.act-solutions.com/ICC/pdfs/psg/psg_spec.pdf

RandEngi
07-01-2008, 02:17 AM
Volts / Resistance = Current
Volts / Current = Resistance

12V / 0.004A = 3000 ohms
12V / 0.02A = 600 ohms

Use a potentiometer with range 600 to 3000 ohms in serial to produce the wanted current. Tho it would probably be easier to just buy the one from Kele or ACT

orion242
07-01-2008, 08:14 PM
You have to also take into account the impedance of the input on the device you’re testing, which will vary between devices.

If you’re willing to whip out a soldering iron, the AD694 is a cheap IC that can do exactly what you want. With a few parts and a DC power supply (ie battery) it will drive a 4-20ma signal that will be consistent with different devices attached to it.

Here is a diagram.

http://forums.parallax.com/forums/attach.aspx?a=3066