johnzo1995
05-18-2008, 09:30 PM
Two weeks ago, I installed a 3.5 Rheem R22 Heat Pump. Im having problems in which the unit is not cooling. The unit was factory charged for 15 feet of line. I added an additional ~1 lb for the extra lenght of line.
The unit does not cool very good at all, I'm getting only a delta T of 10 degrees arcoss the evaporator. The condensor came with a charging table on the inside cover. The pressures are right on. However the subcooling is ~25 degress. I didn't check superheat and the suction line was not cold at all. I'm thinking the TXV is faulty and is not metering the refrigerant correctly.
Another weird thing happend, since it was a heat pump I which it over to heat. I worked great for about 10 mintues, then the high side (low side in cooling) pressures went up very high and rapidly fluctuating between 350-400psi.
Every thing is brand new including the line set, installed to industry standards.
Sorry this is not in the pro forum, any suggestions would greatly be apreciated.
The unit does not cool very good at all, I'm getting only a delta T of 10 degrees arcoss the evaporator. The condensor came with a charging table on the inside cover. The pressures are right on. However the subcooling is ~25 degress. I didn't check superheat and the suction line was not cold at all. I'm thinking the TXV is faulty and is not metering the refrigerant correctly.
Another weird thing happend, since it was a heat pump I which it over to heat. I worked great for about 10 mintues, then the high side (low side in cooling) pressures went up very high and rapidly fluctuating between 350-400psi.
Every thing is brand new including the line set, installed to industry standards.
Sorry this is not in the pro forum, any suggestions would greatly be apreciated.