05-03-2008, 01:25 PM
hi everyone, I am still having trouble setting the superheat on low temp equipment. I am working on a two door reach in freezer and need to adjust the expansion valve or at least make sure it is working properly. I usually wait until inside temp is around 8 degrees before I start checking superheat the goal is a 0 degree box. Can you guys help me and give me your ideas and your proceedure for adjusting superheat on low temp. Thanks for any help, Paul

nightranger121
05-04-2008, 08:36 PM
A quick check on the TXV would be to stick the bulb in a cup of hot water... your suction pressure should rise within a few seconds. Actual superheat for that coil, I believe, should be around 4 to 6 degrees or so.

powell
05-05-2008, 09:20 AM
hi everyone, I am still having trouble setting the superheat on low temp equipment.

Pauuly,

What troubles are you having?

Pauuly48
05-05-2008, 09:32 AM
I am having trouble with the math for example a negative 10 degree coil and a 6 degree superheat would I need 4 degrees on my pipe temp.?

smilies
05-06-2008, 01:02 AM
I am having trouble with the math for example a negative 10 degree coil and a 6 degree superheat would I need 4 degrees on my pipe temp.?

That would be -4*F.

Pauuly48
05-06-2008, 12:14 PM
Thanks makes sense now.