View Full Version : XL-50 status "stop"



justafitter
04-24-2008, 07:42 PM
I have airhandler with xl-50 was working fine until the other day when I had steam valve actuator fail and went off on high supply temp. Changed actuator, cleared alarms, now I dont know how to restart application. Shows application stopped but mode is occupied so fans etc should run. Unit operates normally in manual modes for DO and AO points (fans,valves,etc). I have no prior experience with these controllers, any help appreciated.

lwarren
04-24-2008, 08:50 PM
Have you tried cycling power on the XL50?

justafitter
04-25-2008, 05:57 PM
Thanx lwarren, I cant beleive I didn't try that, god knows I tried everything else (except for the reset button which I knew would lose the program I dont even have a copy of). Thanx a Bunch

lwarren
04-25-2008, 06:03 PM
No problem, glad it worked.

I have a bunch of those at one particular site and everytime a storm comes through the application just stops and the customer has to go around and cycle power to them.

mandrake
04-27-2008, 04:43 AM
you ought to flash the application to flash memory, especially if you don't have the project backup

underrock
04-30-2008, 02:05 PM
I have airhandler with xl-50 was working fine until the other day when I had steam valve actuator fail and went off on high supply temp. Changed actuator, cleared alarms, now I dont know how to restart application. Shows application stopped but mode is occupied so fans etc should run. Unit operates normally in manual modes for DO and AO points (fans,valves,etc). I have no prior experience with these controllers, any help appreciated.

What are you using to talk to the XL50 with. You may be able to make a basic backup.

justafitter
05-04-2008, 07:17 PM
I don't have a laptop or software. I guess I could have customer go back on installing company to get software backup.