PDA

View Full Version : RTAA- History Memory Error Type 1 Message



b-man
04-14-2008, 08:38 PM
Got a call to troubleshoot RTAA chiller. Faults are
1) History Memory Error Type 1
2) Compressor Overload Setting Alarm
Haven't worked on RTAAs before and am digging up manuals. Any heads up advice on these faults. Heard I might have a board failed.

PJ's cool-aid
04-14-2008, 10:11 PM
the book says ucm is operating on ROM default for all setup parmeters. check all setup parameters and continue to run chiller. the default overload setting must not match the dip swich settings. you can get the IOM from the trane web site RTAA-10M-4A. If the settings don't stay in the module then a replacment will be needed.

b-man
04-17-2008, 06:50 AM
PJ's cool-aid
Thanks. Got the manual and info I needed.