View Full Version : Counterflow oil



tomt
03-23-2008, 05:30 AM
I do not do residential work so could use some help here.Have a upflow oil fired furnace, ductwork comes out the top elbows down to floor runs under house.Want to replace with a oil fired counterflow furnance.
Question: already have new 3 ton coil and condenser,does coil have to be on the supply side of furnance or can it be in the return.
Has open return, putting in ducted return above ceiling.

bob hubbard
03-23-2008, 07:17 AM
yes , The coil needs to be on the bottom of a cf furnace . Also you need a coil that rated for downflow such as a heatpump coil .

tomt
03-26-2008, 05:29 PM
Thanks for setting me straight on this one, do not want to have any problems.