View Full Version : Liebert Sitelink alternative
Working on an AX Supervisor project interfacing with all sorts of Data Center equipment. Getting around to hooking up 18 Leibert System 3 units that will require using 2 Sitelink-12 panels. Liebert wants $8500 for the panel. The sitelink panels look to be an OEM version of the ALC LGNet panel. We also got a price on the Opencomm NIC for $1400 each. Has anyone found another way to communicate with the native RS422 Liebert bus?
bobby m
01-24-2008, 05:48 PM
Fieldserver ?
Didn't see Liebert in the Fieldserver driver list. The Liebert RS422 port uses a proprietary protocol.
Did find the plug-in opencomms card for around $300 each. Unfortunately we need the card with adapter.
Daisey chain the devices and set the IDs per Opencomms instructions.
Try a "Modbus Async Network" on a Jace. Set the "Data Mode" to RTU, set the serial port correctly and get the modbus registry from Liebert and you should be in.
Daisey chain the devices and set the IDs per Opencomms instructions.
Problem is the units don't have the Opencomm cards installed, just the native Liebert port.
sysint
01-25-2008, 07:57 AM
Daisey chain the devices and set the IDs per Opencomms instructions.
Try a "Modbus Async Network" on a Jace. Set the "Data Mode" to RTU, set the serial port correctly and get the modbus registry from Liebert and you should be in.Why aren't you recommending trying to jam a BCU on the system?
Ohh let me think about this..........a Jace would do the job if there were Opencomms cards and a BCU won't........and if I come across a BCU to jam somewhere YOU will be the first to know..:D:eek:
sysint
01-25-2008, 04:14 PM
You are learning. I know it's slow because you are (were?) a Trane guy, but you are making some progress. Keep trying. I see Trane is using LNS now so you can say that is OK.
Isn't the LG box a gateway?
hotrod53
01-31-2008, 07:45 PM
You are correct about the ALC OEM, they are made by ALC. As an ALC dealer, I can't buy them either. There is a way to sequence them hard-wired, Liebert sells a sequencer that does this that is only a relay sequencer. As far interfacing, their protocol is called IGM, we read it right out of the Sitelink module. Typically there is a plug that you have to swap in the cabinet and you connect to a terminal block on 77-78 or 78-79, I forget, but there is only these two terminals on that block. You also have to program the keypad to tell it to speak IGM. If you don't have the interface I think that you are out of luck.
ddcctrl
07-02-2008, 11:41 AM
Hello Krac:
Can you contact me concerning what your solution was for this? I have similar opportunity. Please see email and IM info in profile. Thanks.
The customer ended up buying the opencomm cards.