View Full Version : ZN510 Alarm Message



dapper
01-24-2008, 02:11 PM
I'm looking for a description of the alarm messages in the zn510. The one I am currently recieving just says 'Maintenance'. Does this indicate short cycling? or some other problem. Any reference to the alarm messages would be appreciated.

scrooloose
01-24-2008, 02:14 PM
I believe Maintenence Req alarm is just a run timer that is set in the controller. After x hours the Maint Alarm comes in, used for filter/belt checks, etc..

If you dont need this function i believe you can just set the timer to 0 to disable it.

roadgear16
01-24-2008, 10:31 PM
maintenance timer is defaulted to 600 hours. As scrooloose said, you can set this value to 0 (with Rover) to avoid alarms in the future. From Summit, you can reset the maintenance timer in the device editor.

kwillmech
01-24-2008, 10:57 PM
maintenance timer is defaulted to 600 hours. As scrooloose said, you can set this value to 0 (with Rover) ...

Or use the Trane LNS plugins available here (http://www.trane.com/Commercial/DesignAnalysis/DownloadCenter.aspx?i=909) in the Building Controls section.


kw

dapper
01-25-2008, 07:55 AM
Thanks for the info guys. When I stop at the job today I will reset the timers or zero them out with through the plug-ins.